| Line 449: | Line 449: | ||
{{:Configurable EUT Controller}} | {{:Configurable EUT Controller}} | ||
===Auxiliary equipment=== | |||
{{:Configurable equipment}} | |||
==Messages == | ==Messages == | ||
Device drivers[edit]
Virtual device drivers[edit]
- Usable frequency range
- Maximum input power
Signal generator[edit]
Amplifier[edit]
Antenna[edit]
Coupler[edit]
Powermeter[edit]
| The minimum time that should be waited before the measurements starts. |
| The minimum amount of measurements that RadiMation® has to perform to determine if the <Max. Difference> condition is met. |
| The minimum time that RadiMation® should be waiting between each measurement. |
| The maximum difference that is allowed between the <Measure> measurement value(s); the highest and the lowest values are compared. |
| The maximum amount of measurements that could be performed by RadiMation®, before there is a final measurement value available (which could meet these conditions, or not). |
Speed up(2): When using a spectrum analyser a small amount of samples may be sufficient to determine the right amount of power. It is up to the engineer to find the right accuracy vs. time setting. Measuring: Powermeters which do not have a RMS detector, should not be used in Fast constant mode. |
Field Sensor[edit]
Axis setting panel[edit]
AD converter[edit]
Injection device[edit]
Calibration Jigs[edit]
Current Sensor[edit]
Pre Amplifiers[edit]
LISN[edit]
Turn Table[edit]
Antenna Tower[edit]
Absorbing Clamps[edit]
Clamp positioner[edit]
Cables[edit]
Switch matrix[edit]
EUT Controller[edit]
Auxiliary equipment[edit]
When a Auxiliary equipment can be remotely controlled the specific window will appear. Please view chapter IEEE or RS232 setting for a complete description. When the Auxiliary equipment can not be remotely controlled the message This Device cannot be configured will appear.
Different test and measurement instrumentation devices, can be controlled by different electronic communication buses and connectors, with on top of that different communication protocols. Which communication stream setting should be used to control a measurement instruments, cannot be easily based alone on the connector that is used to connect the measurement instrument. The following list shows the possible communication interfaces and protocols that are possible with a specific connector. This table can help to identify the actual communication protocol that is used. The manual of the test and measurement instrument also often lists the communication protocol that should be used, with similar terms, as is shown in the table. Based on the actual communication protocol the best communication stream to use is suggested.
| Connector | Communication protocol | Suggested communication stream | Alternative communication stream |
| GPIB / IEEE-488 | GPIB | GPIB | VISA (with GPIB sub option) |
| Ethernet / RJ45 | VXI-11 | VISA (with LAN sub option) | |
| HiSLIP | VISA (with LAN sub option) | ||
| Raw socket | TCPIP | VISA (with Visa-ID sub option with ::SOCKET identifier)
| HTTP | HTTP | ||
| UDP | UDP | ||
| USB | Virtual COM Port (VCP) (RS-232) | RS-232 | VISA (with RS-232 sub option) |
| USBTMC (Test and Measurement Class) | VISA (with Visa-ID sub option) | ||
| Raditeq USB devices | USB | RS-232 VISA (with RS-232 sub option) | |
| Device specific USB | should be implemented device specifically | ||
| Sub-D9 / RS-232 | RS-232 | RS-232 | VISA (with RS-232 sub option) |
| other software | Raw socket | TCPIP | VISA (with Visa-ID sub option with ::SOCKET identifier)
The details for the configuration of each possible communication stream is described in the next section.
Communication settings[edit]
GPIB Setting[edit]
| The primary address specifies the address of the device, so if the device you want to configure is on address 20 you enter 20. Please consult the manual of the device how to determine the GPIB address of the device. |
| Allows the end-user to enable the more advanced configuration parameters. Those advanced option should only be used if the default settings are not sufficient. |
| The second address is 0 by default, and should only be changed when needed. For further information please look in the help of National Instruments 488.2. |
| GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast PCs (> 2.5 GHz). This is most of the time noticeable when a driver is sometimes working and sometimes gives a GPIB (EABO or TIMO) error. These errors are most of the time, generated randomly. Specifying a GPIB delay time of 3000 uSeconds can fix these random errors. Run the test again and see if the problem has disappeared. If the problem has disappeared then your problem was timing, if not please contact your reseller and report the problems you are having. |
| When checked, a low level GPIB command to reset the device will be sent to the device during initialisation. |
| When checked, a low level GPIB command to select the correct address will be transmitted every time a command is sent to the device. |
HTTP Setting[edit]
| Allows to specify the IP-address or the (FQDN) hostname and the socket port number of the measurement device. This is normally done with a string like: "tcpip://<address-or-name>:<port-number>", where '<address-or-name>' is the IP address or hostname, and '<port-number>' is the socket port number on which the connection should be initiated. By default the socket port number is 80, but this can be changed to another port if desired. |
Manual Setting[edit]
The manual communication stream can be used to show message boxes on the screen for the end-user, to manually perform some operation on a device. The commands that are specified in the device driver that is using the manual communication stream, are thus the messages that are shown to the end-user in a message box, for example with the instruction to change a setting on a test and measurement device.
No further configuration in the manual communication stream is needed.
RS-232 Setting[edit]
The RS-232 communication settings specify the serial port parameters when communicating with a measurement device over RS-232. Although many modern devices connect via USB, they often appear as a virtual COM port (VCP). In that case you still configure the RS-232 settings as below.
| The COM port which RadiMation® has to be used to communicate with the measurement device. |
| Allows to configure the baud rate that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
| Allows to configure the number of data bits that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
| Allows to configure the parity bit that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
| Allows to configure the number of stop bits that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
| Allows to configure if and which terminator should be used during data transmissions to the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
| Allows to configure if and which terminator should be used during the receiving of data from the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
| Allows to configure if a read should be ended as soon as the receive terminator is received from the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
RSIB Setting[edit]
| Allows to specify RSIB identifier of the device that should be controlled. |
TCPIP Setting[edit]
| Allows to specify the IP-address or the (FQDN) hostname and the socket port number of the measurement device. This is normally done with a string like: "tcpip://<address-or-name>:<port-number>", where '<address-or-name>' is the IP address or hostname, and '<port-number>' is the socket port number on which the connection should be initiated. If the socket port number is a fixed port number, it is already shown as the default value, and it will be automatically added when no socket port number is specified. |
UDP Setting[edit]
The UPD communication settings are used to specify that an UDP based communication over ethernet should be used to control the measurement.
USB Setting[edit]
| The device identifier (which is a unique identifier of 8 groups of digits) that identifies the measurement device that is connected over USB. |
| Will automatically determine the correct Device Identifier for the measurement device that is connected. |
VISA Setting[edit]
| Allows to specify a VISA Alias that should be used for the communication with the measurement device. Any Alias that is supported by VISA is accepted. The correct Alias can be determined by using the VISA manager (eg. National Instruments MAX or Keysight Technologies connection expert) that is installed on the PC. |
| Allows to specify that GPIB should be used for the communication with the measurement device. The GPIB address of the measurement device should be specified. |
| Allows to specify that a VXI-11 or LXI connection should be used for the communication with the measurement device. It is possible to specify the IP-address or the (FQDN) hostname of the measurement device. |
| Allows to specify that a RS232 (ASRL in VISA terms) connection should be used for the communication with the measurement device. The COM port of the measurement device should be specified. |
Allows to specify a VISA Identifier that should be used for the communication with the measurement device. Any VISA Identifier that is supported by VISA is accepted. If one of the other communication methods is selected the corresponding VISA Identifier is also shown in this setting. Often used VISA identifiers are:
- Press the “New” button.
- The name of the device driver will be added in the available device drivers list.
- Select the new device driver from the available device drivers list.
- Press the “Edit” button.
Generic settings[edit]
| The default value for the start frequency is 1 Hz and for the stop frequency is 120 GHz. The creator of the device is encouraged to set the correct start and stop frequency. If the start and stop frequency are set correctly, RadiMation® can warn the test engineer when they want to use the device out of its valid frequency range. |
| In the reset window you need to specify the string that the software needs to send when it want to reset the device. For example *RST is commonly used reset string. If you don’t know the string then leave this window blank, and make sure that the device in a neutral state. |
| In the init window you need to specify the string that the software needs to send when it want to Init the device. For example *RST is commonly used reset string. |
| In the Get ID window you need to specify the string that the software needs to send when it wants to get the ID string of the device. For example *IDN? is commonly used Get ID string. |
| In the Returned ID window you need to specify the string that the software will receive so that it knows that it has the right device. For example "Hewlett_Packard,8643A," can be used for the Hewlett Packard 8643A. If you leave this window empty then all returned strings are accepted. |
| Set Frequency is the string that needs to be sent to set the signal generator frequency. The unit is in MHZ, so the string should be made for MHz. |
Example: “FRQ__freq__MHZ”.
Example: “FRQ__freqHz__HZ”.
Example: “FRQ__freqkHz__KHZ”.
Example: “FRQ__freqMHz__MHZ”.
Example: “FRQ__freqGHz__GHZ”.
| Set Carrier is the string that needs to be sent to set the signal generator carrierlevel. The unit is in dBm, so the string should be made for dBM. |
| Carrier on is the string that needs to be sent to set the signal generator carrier on. |
Example: “OUTPUT ON”.
| Carrier off is the string that needs to be sent to set the signal generator carrier off. |
Example: “OUTPUT OFF”.
| AM on is the string that needs to be sent to set the internal AM generator of the signal generator. The unit of frequency is KHz and the unit of Modulation Depth is %. |
| AM off is the string that needs to be sent to set the internal am modulation of the signal generator off. |
| External on is the string that needs to be sent to set the modulator to the external input. |
| External off is the string that needs to be sent to set the modulator to the internal input. |
| PM on is the string that needs to be sent to set the internal PM generator of the signal generator. The unit of frequency is KHz and the unit of duty cycle is %. |
| PM off is the string that needs to be sent to set the internal PM modulation of the signal generator off. |
| Sine wave is the string that needs to be sent when RadiMation® wants to set the wave form of the internal source to sine. |
Example: “SOURCE2:FUNC SIN”
| Square wave is the string that needs to be sent when RadiMation® wants to set the wave form of the internal source to square. |
Example: “SOURCE2:FUNC SQU”
Configurable Amplifier[edit]
Main[edit]
Operation[edit]
Example[edit]
Configurable Antenna[edit]
Configurable Powermeter[edit]
| Set Frequency is the string that needs to be sent to set the powermeter frequency. The unit is in MHz, so the string should be made for MHz. |
Example: “P1,U1”.
Example: “X1”
| Result Format is the string that RadiMation® needs to use to decode the value from the string sent by the powermeter. The return value is interpreted in dBm. |
Example: “__result__”
Example: “O1”
| Duration is the time that RadiMation® waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable results. |
Channels[edit]
Read Back examples[edit]
Communication[edit]
| The lowest usable frequency of the device. |
| The highest usable frequency of the device. |
The impedance of the injection system itself, for which the calibration jig is used to calibrate it.
Configurable LISN[edit]
| The reset command that needs to be send to device. When left blank, no command will be send. |
| The command that is send to retrieve the identity of the device. This is used to check if the device is connected. A commonly used SCPI command is: *IDN?. When left blank, no command will be send, and the device check is skipped. |
| A string that is used to check if the correct device driver is selected and the device is connected. The device check consists of a few steps. First the Get ID command is transmitted to the device, and the response from the device is then received. The received response is then searched for the string specified at Returned ID, and if the string is found it is confirmed that the correct device is connected. The string specified can also be a Regular expression, which is then used to find a match in the response from the device. Leaving this blank, will skip the device check, and it is silently assumed (but not checked) that the correct device is connected. |
| The command that should be transmitted when the 'Neutral' line of the LISN should be selected. If no command is specified, nothing will be transmitted. |
| The command that should be transmitted when the 'Line 1' line of the LISN should be selected. If no command is specified, nothing will be transmitted. |
| The command that should be transmitted when the 'Line 2' line of the LISN should be selected. If no command is specified, nothing will be transmitted. |
| The command that should be transmitted when the 'Line 3' line of the LISN should be selected. If no command is specified, nothing will be transmitted. |
| Closes the dialog, where all the changed settings are stored. |
| Closes the dialog, where all the changed settings are discarded. |
| Opens an additional dialog which allows to set the correct communication medium to communicate with the device, including any relevant settings. |
Configurable Turn Table[edit]
Configurable commands[edit]
Check device[edit]
Device is initialised[edit]
Device is deinitialised[edit]
Some examples are:
| Received information | Regular expression | RadiMation® Readout | Note |
Communication[edit]
Identification[edit]
Antenna Tower[edit]
| The command that is send to stop the antenna tower. When left blank, no command will be send. |
| The command that is send to request the current height. When left blank no command will be send. |
| A regular expression to parse the response from the Current Height request. The received value will be interpreted as being the the unit in Meter, Centimeter or Millimeter, as selected by the dropdownbox. |
| The command that is send to move the antenna tower to a certain height. The command must include a keyword, __meter__, __centimeter__ or __millimeter__ which will be replaced with the corresponding height for the antenna tower. When left blank, no command will be sent. |
| The command that is send to request the status if the antenna tower is moving. When left blank, no command will be send. |
| A regular expression which will be matched against the response of the Position stopped command. When the result is matching with the response, the tower is stopped. |
| The command to request the current polarisation. It is mandatory to also supply the format of the polarization in the next fields. When left blank, no command will be sent. |
| A regular expression which will be matched against the response of the Current Polarization command. When the result is matching the driver reports Horizontal back to RadiMation. |
| A regular expression which will be matched against the response of the Current Polarization command. When the result is matching the driver reports Vertical back to RadiMation. |
| The command that is send to change the polarization to horizontal. When left blank, no command will be send. |
| The command that is send to change the polarization to vertical. When left blank, no command will be send. |
| The command that is send after the command Hor. Polarization is sent, with a delay of Waiting time between the two commands. When left blank, no command will be send. |
| The command that is send after the command Vert. Polarization is sent, with a delay of Waiting time between the two commands. When left blank, no command will be send. |
| The wait time, specified in milli seconds, between the Polarization command and Polarization stopped commands. |
Antenna Tower Advanced[edit]
| When checked, no height related commands and changes will be send to the antenna tower. This can for example be checked if the the antenna is mounted on a fixed height tripod. |
| When checked, no polarisation related commands and changes will be send to the Antenna Tower. This can for example be checked if the antenna tower does not have a automatic polariser. |
| When checked, the antenna will be moved to the Start position before the actual test is started. |
| The height, specified in centimeters, to which the antenna is moved, before the actual test is started. |
| When checked, the antenna will be moved to the End position after the test has finished. |
| The height, specified in centimeters, to which the antenna is moved, after the test has finished. |
| The time, specified in seconds, to wait after a command is issued to change the polarisation. This can for example be used to include an additional delay to ensure that the antenna polariser has reached the final location before the actual test continues. |
Currently unavailable.
Configurable Cable[edit]
| keyword | inserted value |
| __freq__ | The signal generator frequency expressed in MHz |
| __freqHz__ | The signal generator frequency expressed in Hz |
| __freqkHz__ | The signal generator frequency expressed in kHz |
| __freqMHz__ | The signal generator frequency expressed in MHz |
| __freqGHz__ | The signal generator frequency expressed in GHz |
| __carrier__ | The signal generator carrier level expressed in dBm |
| __carrierdBm__ | The signal generator carrier level expressed in dBm |
| __carrierW__ | The signal generator carrier level expressed in Watt |
| __carriermW__ | The signal generator carrier level expressed in milli-Watt |
| __forward__ | The forward power expressed in dBm |
| __forwarddBm__ | The forward power expressed in dBm |
| __forwardW__ | The forward power expressed in Watt |
| __forwardmW__ | The forward power expressed in milli-Watt |
| __reflected__ | The reflected power expressed in dBm |
| __reflecteddBm__ | The reflected power expressed in dBm |
| __reflectedW__ | The reflected power expressed in Watt |
| __reflectedmW__ | The reflected power expressed in milli-Watt |
| __height__ | The height where the antenna is moving to expressed in metre |
| __heightm__ | The height where the antenna is moving to expressed in metre |
| __heightcm__ | The height where the antenna is moving to expressed in centimetre |
| __angle__ | The angle where the turntable is turning to expressed in degrees |
| __degree__ | The angle where the turntable is turning to expressed in degrees |
| __radian__ | The angle where the turntable is turning to expressed in radians |
| __calculatedvoltage__ | The calculated voltage expressed in V. |
| __<InformationItemName>__ | The value of the corresponding EUT or General information item. |
Messages[edit]
Unknown Device Driver[edit]
Device not connected[edit]
How to Report an Error[edit]
AD convertors[edit]
Type of communication: IEEE.
Channels 1:
Hewlett Packard 34401A[edit]
Channel 1
Type of measurement: AC Volt
Minimum value: 0Volt
Maximum value: 1 kVolt.
Channel 2:
Minimum value: 0 Amp.
Maximum value: 3 Amp.
Channel 3
Type of measurement: DC Volt
Channel 4:
Maximum value: 3 Amp. (rms)
Channel 5
Minimum value: 0 Ω
Maximum value: 100 MΩ
Channel 6
Minimum value: 0 Hz.
Maximum value: 300 kHz
Channel 7 and 8
Not used
Hewlett Packard 54600[edit]
Channel 1:
Type of measurement: V Max.
Maximum value: 1000 Volt.
Channel 2:
Type of measurement: V Min
Minimum value: 0 Volt.
Channel 3
Channel 4:
Channel 5
Minimum value: 0 Hz
Maximum value: 100 kHz
Channel 6
Type of measurement: Period
Minimum value: 0 ms
Maximum value: 10000 ms
Channel 7
Minimum value: 0 ms
Channel 8
Minimum value: 0 ms
Hewlett Packard 3562A[edit]
Type of communication: GPIB
Channels
Minimum value: 0 dB
Maximum value: 100 dB
Hewlett Packard 59313[edit]
Channel 1
Minimum value: 0
Maximum value: 2048
Channel 2:
Minimum value: 0
Maximum value: 2048
Channel 3
Minimum value: 0
Maximum value: 2048
Channel 4:
Minimum value: 0
Maximum value: 2048
Channel 5 to 8
Not used.
Channels
Marconi 2305[edit]
Channel 1
Minimum value: 0
Maximum value: 1000 MHz
Channel 2:
Minimum value: 0
Maximum value: 1000
Channel 3 to 8
Not used.
Fluke 45 AC Current[edit]
Channels
Minimum value: 0 mA
Maximum value: 10.000 mA
Fluke 45 DC Current[edit]
Channels
Minimum value: 0 mA
Fluke 45 AC Voltage[edit]
Channels
Minimum value: 0 mV
Maximum value: 1.000.000 mV
Fluke 45 DC Voltage[edit]
Channels
Minimum value: 0 mV
Fluke 45 Frequency[edit]
Channels
Minimum value: 0 Hz
Maximum value: 1.000.000 Hz
Fluke 45 Resistance[edit]
Channels
Minimum value: 0 Ω
Maximum value: 100.000.000 Ω
Channel 1
Maximum value: 353.55 Volt.
Channel 2:
Channel 3
Channel 4:
Maximum value: 707.1 Volt
Channel 5
Type of measurement: RMS
Maximum value: 250 Volt
Channel 6
Maximum value: 200 MHz
Channel 7 and 8
Not used
Fluke 8840A AC Current[edit]
Channels
Minimum value: 0 mA
Fluke 8840A DC Current[edit]
Channels
Minimum value: 0 mA
Fluke 8840A AC Voltage[edit]
Channels
Minimum value: 0 mV
Fluke 8840A DC Voltage[edit]
Channels
Minimum value: 0 mV
Channels
Minimum value: 0 mA
Channels
Minimum value: 0 mA
Channels
Minimum value: 0 mV
Maximum value: 300.000 mV
Channels
Minimum value: 0 mV
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Channels 1 to 8
Minimum value: 0
Maximum value: 16383
EIP 575[edit]
Channel 1
Minimum value: 0 Hz
Maximum value: 10 kHz
Channel 2:
Channel 3
Minimum value: 0 Hz
Maximum value: 1 MHz.
Channel 4:
Maximum value: 10 MHz.
Channel 5
Minimum value: 0 Hz
Maximum value: 100 MHz
Channel 6
Minimum value: 0 Hz
Maximum value: 1 GHz
Channel 7
Minimum value: 0 Hz
Maximum value: 10 GHz
Channel 8
Minimum value: 0 Hz
Maximum value: 100 GHz
Channel 1 to 8