Line 327: Line 327:
Calibration procedure:
The IEC 1000-4-6 is based on an EUT cable impedance of 150 Ω. To calibrate the test system, a cable with a characteristic impedance of 150 Ω is used. This reference cable is placed in the injection clamp. The left side of this cable is terminated through a 150 Ω terminator resistor. The right side of the cable is terminated with a 100 Ω resistor in series
The IEC 1000-4-6 is based on an EUT cable impedance of 150 {{Ohm}}. To calibrate the test system, a cable with a characteristic impedance of 150 {{Ohm}} is used. This reference cable is placed in the injection clamp. The left side of this cable is terminated through a 150 {{Ohm}} terminator resistor. The right side of the cable is terminated with a 100 {{Ohm}} resistor in series
with a 50 Ω power meter. The measured power in the 50 Ω powerhead can be used to calculate the RF current in the 150 Ω reference wire.
with a 50 {{Ohm}} power meter. The measured power in the 50 {{Ohm}} powerhead can be used to calculate the RF current in the 150 {{Ohm}} reference wire.
If an amplifier with a 50 {{Ohm}} output impedance is used in conjunction with a injection clamp with a 50 {{Ohm}} input impedance, the voltage applied to the input of the injection clamp will be [Urms/2].
The current injected in a 150 {{Ohm}} wire will be [Urms/2] / 150 {{Ohm}}.
By measuring the voltage across the 50 {{Ohm}} powerhead, the calibration software determines the signal generator level which generates the desired current in the reference cable.
<math>U_{powerhead}=U_{rms} - 6[dB]-20*^{10}Log\frac{50}{150}= U_{rms}-15,6[dB]</math>
Line 344: Line 344:
'''Example:'''
'''Example:'''
Test level according to IEC 1000-4-6 : 10 Vrms (140 dBuV) Measured value (U powerhead) : 140 dBuV - 15,6 dB = 124 dBuV or = 17 dBm (in a 50 Ω system)
Test level according to IEC 1000-4-6 : 10 Vrms (140 dBuV) Measured value (U powerhead) : 140 dBuV - 15,6 dB = 124 dBuV or = 17 dBm (in a 50 {{Ohm}} system)
Line 398: Line 398:
Verification procedure:
After a calibration has been carried out, the calibrated test set-up can be checked by the following procedure. The same set-up is made as during calibration. As an extra check, a measuring current probe is placed around the 150 {{Ohm}} reference wire. After the calibration has been completed, a radiated immune, substitution test is made with a test level of 10 Vrms.
The theoretical current with a test level of 10 Vrms will be:  (Urms/2) / 150 = 33 mA
When a current probe with an transfer impedance of 1 Ω is used, a voltage of 33 mV should be measured (or ~90 dBuV).
When a current probe with an transfer impedance of 1 {{Ohm}} is used, a voltage of 33 mV should be measured (or ~90 dBuV).
Revision as of 17:39, 12 January 2009
During a calibration, RadiMation® stores all equipment under test used during the calibration. If the test equipment used can return it’s serial number through the IEEE bus, this serial number will be recorded.
Furthermore, all settings (like start frequency, stop frequency, probe response time, frequency step size, calibration type (FWD, transmitted or signal generator level, etc.) are recorded.
  • The achieved field strength (or current) during calibration.
  • The signal generator level, necessary to achieve this field strength (or current level)
  • The Forward power, necessary to achieve this field strength (or current level)
  • The transmitted power, necessary to achieve this field strength (or current level)
Note: When a signal level calibration is made and no power meters are used, the forward and reflected power graphs are not stored.
When a forward power calibration is made and no reflected power meter is used, the reflected power graph is not stored.
All can be viewed and printed by the operator.
To view calibration data, open the calibration file through the File, Open, calibration pull down menu. When a calibration window is opened, the calibration configuration data, as well as the Equipment used, is displayed.
Frequency interpolation of Calibration files[edit]
RadiMation® allows you to use a frequency step size during a test, which is smaller than the frequency step size during the calibration. For this purpose RadiMation® uses a linear interpolation between the frequency point which is just below the desired test point and the frequency point which is directly above the test point. Of coarse frequency interpolation will reduce the accuracy of the test level, and should therefore only be used during pre-compliance tests.
Amplitude extrapolation of calibration files[edit]
RadiMation® allows you to run a test at a different test level as used during the calibration. For this purpose RadiMation® uses a linear extrapolation from the calibration level to the desired level.
If, for example at a certain frequency point 100 Watt (+50 dBm) is needed to generate a field of 10 V/m (which is determined during calibration) and one wants to use this calibration file to run a test at 3 V/m, RadiMation® will use a power level of 50 DBm - 20 log (10/3) = 40 dBm (10 Watt). Of coarse, amplitude interpolation will reduce the accuracy of the test level and should therefore only be used during pre-compliance tests.
Warning: The amplitude extrapolation will only be correct if the power amplifier works in its linear region.
RadiMation® supports three different ways of power calibration. During the configuration of the calibration, the desired method should be selected. During a test, when a calibration file is selected, RadiMation® automatically selects the method used during calibration.
Calibration methods[edit]
During signal generator level calibration only the signal generator level is recorded during the calibration. This method does not take amplifier instability into account. During this calibration method no power meters are required. This method is less accurate than the FWD power and transmitted power calibrations and therefore not recommended for full compliance tests.
During a Forward power calibration, the forward power to the transmitting antenna is recorded. During a test, the FWD power to the antenna is kept the same as during the calibration. By this method, amplifier drift will have no influence on the test.
Net power calibration[edit]
During a Net power calibration, the Forward and Reflected power to the antenna are recorded. The difference between the FWD power and Reflected power is the Transmitted power. During a test, the Transmitted power is kept the same as during calibration. When a large metallic, EUT is placed in front of the antenna, some RF energy is reflected back into the antenna, resulting in a worse VSWR. When only FWD power is calibrated, this effect is not compensated for. When transmitted power is calibrated, the by the antenna transmitted power is kept the same as during calibration.
Radiated immunity calibration[edit]
Calibration of the radiated immunity test set-up is necessary when tests in accordance to the substitution method are performed. During a substitution test, first the empty anechoic room is calibrated (i.e.: the power to the transmitting antenna is recorded which is necessary to achieve the desired field strength in the room). During the test the EUT is placed inside the anechoic chamber, and the same power is applied to the transmitting antenna.
One-point calibration[edit]
During a 1-point calibration, RadiMation® for each frequency point increases the power to the antenna, until the desired field strength is reached. Then, depending on the type of calibration RadiMation® records the Signal generator level, FWD power and/or transmitted power in the calibration file. To start a radiated immunity one-point calibration please select:
   Menu.svg Calibration
      Menu.svg Radiated Immunity
         Menu.svg 1 Point Calibration
File:Select TSF File 1 Point Calibration Window.png
Device name Tab in RadiMation®configuration window
Signal Generator Standard 1
Amplifier Standard 1
Coupler Standard 1
Power meter Pfwd Standard 1
Power meter Refl Standard 1
Antenna Standard 1
Field sensor Field probes
Cables
1 Sign-> Amp Cables
2 Amp-> Coupler Cables
3 Coup->Ant Cables
4 Coup->Pfwd Cables
5 Coup->Pref Cables
16 point field homogeneity verification / Uniform Field Area calculation[edit]
The EN 61000-4-3 (and other standards) states that the anechoic room must have a homogeneous field distribution in a 1.5 m. x 1.5 m. square area, 80 cm. above the ground.
The field is defined as homogeneous if, at 12 of 16 points in the 1.5 m. x 1.5 m. square the field strength lies between the desired value and the desired value plus 6 dB (see the figure below).
For this purpose, sixteen '1 point calibrations' must be performed. After all 16 calibrations are carried out, the 16 point field homogeneity verification software can be used to verify the field homogeneity in the room.
The sixteen-point verification is started by selecting:
      Menu.svg System Calibration
         Menu.svg Radiated immunity
            Menu.svg Uniform Field Area calculation
The user is requested to select a calibration TSF file from the list of available TSF files as shown below.
File:Select TSF File 16 Point Calibration Window.png
After a calibration TSF file is selected a typical 16 point calibration TSF will appear like the one shown in the picture below.
The RadiMation® package supports different ways to calculate the uniformity of a field, to determine the 4 points (out of the 16 points) which must be ignored for each test frequency.
  • EN 61000-4-3 1995 (Average Power)
  • ISO 11451-2
  • J1113-25
  • EN 61000-4-3 2002 (Average Field)
  • EN 61000-4-3 2002 Amendment 1 (Maximum Power)
  • EN 61000-4-3 2006
  1. Use one time averaging
  2. Use four time averaging
One time averaging[edit]
Four time averaging[edit]
  1. The software takes the average of all 16 test-points, and will determine the test point, which differs the most from the average. For this frequency, this point will be removed from the calibration file.
  2. The software takes the average of the remaining 15 test points, and determines the point, which differs the most from this new average. For this frequency, this point will be removed from the calibration file.
  3. The software takes the average of the remaining 14 test points, and determines the point, which differs the most from this new average. For this frequency, this point will be removed from the calibration file.
  4. The software takes the average of the remaining 13 test points, and determines the point, which differs the most from this new average. For this frequency, this point will be removed from the calibration file.
RadiMation® will display 16 coloured dots on the screen, each dot representing a test point in the anechoic room. At the side of these dots, the test frequency can be incremented, which will directly show the new information for the 16 points as represented in the picture below.
  1. Green dot, This point is one of the 12 points, which are taken into account for the calibration file.
  2. Yellow dot, This point is one of the 4 points, which differ the most from the average of the 16 points.
  3. Red dot, This point is one of the 12 remaining points, however, it has an error of more than 6 dB (i.e. the room does not meet the field homogeneity requirements for this point!).
  1. Overall error graph (to verify if 12 of the 16 points lie within the 6 dB error)
  2. Signal generator level graph.
  3. Forward power level graph (only if the forward or net power calibration method is used).
  4. Net power level graph (only if the net power calibration method is used).
  1. Calculated field graphs: When the final calibration file is applied, these graphs display the calculated field for the selected test point location.
  1. Forward power graphs: Forward power used to achieve the desired field strength. This graph is corrected for the calibration (field) uncertainty. If the calibration is made at a test level of 10 V/m with a uncertainty of 1 V/m, the software will calculate the real forward power to achieve exactly 10 V/m (even if the calibration is made at for example 9.4 V/m).
  1. Error graphs: These graphs display the errors for the selected test point location. On frequencies where the test point was not taken into account for the calibration file, the error is set to zero. (i.e. this frequency point is one of the 4 points which where ignored).
Calibration information that is stored after verification[edit]
Now that RadiMation® has determined the homogeneity, what is the information that is stored in the calibration file? And why? The method below describes for the signal generator level but also applies for the forward power and the net power calibration.
The software has determined the remaining 12 points for each frequency according to the chapter '16 point field homogeneity verification'.
Point Signal level (dBm)
1 -10
2 -10
3 -8
4 -12
5 -8
6 -12
7 -8
8 -12
9 -11
10 -9
11 -13
12 -7
The average will give –10 dBm.
This means that with points 3,5,7,10 and 12 you are not generating enough power, because for these points you need a higher signal level. Worst case (number 12), you will generate only around 7 V/m instead of 10 V/m.
That is why RadiMation® saves the highest level in the calibration file.
Triplate calibration[edit]
The triplate calibration needs to be performed in order to perform the triplate test. With the triplate calibration you determine the impedance of the triplate, which is needed to calculate the field.
  1. Some fieldsensors have problems with their ranges, to avoid these problems it is better to field level.
  2. With fixed field you are aways sure that the required level is there, if you use fixed power there may be a big dip or peak in the calibration. This can give interpolation errors. For example a fixed power test at 50 dBm generates a field of 100 V/m at 100 MHz but generates a field of 80 V/m at 800 MHz due to the amplifier/powermeters/cables and couplers. Suppose RadiMation® uses these values to generate a fixed field of 110 V/m. The error made when extrapolation from 100V/m will be much smaller then from 80 V/m.
  3. Error field sensor vs. error powermeter, when performing a fixed power you can have problems with the linearity of your system. In general you can say that your powersensors are better in the linear response then your fieldsensor, so when you are leveling on the field sensor you are sure that the linearity error is reduced to the minimum.
One point calibration[edit]
To start a one-point calibration, close all EUT windows. And select the one point calibration.
A new window will appear, allowing you to set up the calibration. The difference between a chamber calibration and a triplate calibration is the out power. To perform a triplate calibration Net-power needs to be selected as well as outpower.
To define the fieldprobe position in height use the antenna distance. Polarization does not influence this calibration. A description of the rest of the settings can be found in the manual in the chapter 'Radiated immunity calibration'.
Coupler Standard 1
Antenna Standard 1
Cables
1 Sign-> Amp Cables
3 Coup->Ant Cables
4 Coup->Pfwd Cables
5 Coup->Pref Cables
Merge five one point calibration into one final calibration[edit]
         Menu.svg 16 Point Calibration
Formula 12-1: Impedance
Formula 12-2: Middle power calculation
Voltage calibration[edit]
Formula 12-3: Expected powermeter reading
Example:
Coupler Standard 1
Injection device Standard 2
Calibration Jig Standard 2
Sensor power meter Standard 2
Cables
1 Sign-> Amp Cables
3 Coup->Ant Cables
4 Coup->Pfwd Cables
5 Coup->Pref Cables
6 Curr->Sens Cables
Current calibration[edit]
System Calibration[edit]
System calibrations are performed on a test setup, before the test setup can be used to perform the actual measurement. For example:
  1. 1-16 point calibration of anechoic chamber before a radiated immunity test can be performed.
  2. Calibration of conduct immunity setup before a conducted immunity text can be performed.
  3. Open/Short/Through calibration of network analyzer before S-parameter measurement can be performed.
Formula 12 4: Dynamic range
System calibration set up
         Menu.svg Attenuation / Gain
Power meter setting[edit]
Formula 12.5: Average power calculation
Note: The power measurement settings done in the device driver configuration screen are the settings for one sample. This is done because each power meter has a different leveling and measuring time. For the most optimal settings look at the device driver chapter for explanation and tips.
Signal power setting[edit]
  • Dynamic range
  • Reference attenuation
  • Reference noise floor
Formula 12.6: Standard deviation
Formula 12.7: Standard deviation of the dynamic range
Note: Setting the power meter to be infinitely accurate is only valid in a relative measurement. The error caused by the power meter and the signal generator are corrected in the signal generator.
         Menu.svg Gain Compression
Formula 12-8: Average power calculation
Note: When inserting the calibration in the EUT compression configuration the same test levels are used. It is not possible to change the value, so select the settings with care.
EUT calibration set up[edit]
      Menu.svg E.U.T. Calibration
  1. There is no interpolation error possible between frequency points.
  2. The calibration is performed at the same signal generator level preventing extra amplitude errors.
  3. Error budget calculation is possible
  • Dynamic range
  • EUT attenuation
Formula 12 9: Standard deviation of the dynamic range
Formula 12 10: Standard deviation of the attenuation
EUT compression calibrations are performed on amplifiers that are considered to be a EUT. The test goal is to determine the x dB compression point. Yes, you read correctly you can define yourself which compression point you want to measure. It is also possible to measure for example the 1 dB and the 3 dB compression point in 1 test. 12.11.1 EUT Compression Calibration
Before a EUT calibration can be performed, it is best to first perform the system calibration. This will decrees the overall error, which is depending on the devices you are using. The flowchart below describes the testing procedure used for EUT calibration.
General setting guide lines:
  • Signal power amplifier protection should be set high enough for testing. The maximum input level is default 0 dBm when no correction file is attached to the amplifier. With a correction file the maximum input can be set higher then 0 dBm.
  • Forward power amplifier protection should be used when the amplifier has an output power protection. The fail safe option is setting the limitation to the maximum and decrees this with one step size of the test. For example the limitation is set on 56,5 dBm (450 Watt) and the step size is 0.3 dB, than the limitation should be set on 56,2 dBm (420 Watt). This way the changes of the amplifier turning off during testing will become significantly smaller.
  • Start level of the signal generator should be set on 20 dB lower then the lowest point specified by the manufacturer.
  • Stop level of the signal generator should be the maximum input of the amplifier, most of the times this level will not be reached.
Note: Please note that these settings are guidelines, en should be treaded as such.
  • Small signal gain power
  • Compression points power