Line 940: | Line 940: | ||
When a parameter is set to auto, {{RadiMation}} will determine the most optimum settings for this parameter. If the parameter is set to coupled, the parameter will be set to automatic internally in the receiver. | When a parameter is set to auto, {{RadiMation}} will determine the most optimum settings for this parameter. If the parameter is set to coupled, the parameter will be set to automatic internally in the receiver. | ||
{{Warning| When older analyzers and receivers are used that switch between measuring in a linear or logarithmic scale during the pre-scan and final-measurement phases, it is advised to not use a fixed reference level}} | |||
====Max. hold measurements==== | ====Max. hold measurements==== |
Revision as of 09:39, 25 November 2024
Radiated emission[edit]
- Multiband
- Manual Mode
- Burst
- Anechoic chamber
- Fixed height
- GTEM
- Mil Std Magnetic
- Manual mode (Singleband)
- Merge
- X + k * S
Loading a TSF file[edit]
- Tests
- Radiated Emission and then the desired test method.
- Tests
Test results screen[edit]
You can access the test results of the performed test by selecting the test in the EUT window and then press the Info button. For the Multiband test, the window that is appearing looks a lot like the manual mode screen, the reason that it looks the same is because it is. You can continue testing after you finished a test, just select the testsite you want to use and you can continue testing.
Note: | The pass/fail criteria, shown in the tables do not take the measure uncertainty of the test setup into account. |
Note: | Continuing the test is only possible with the selected test site. RadiMation® will not select the correct test site for you. All measurements are done with the selected test site. If you want automatic changes of the test site, restart the configured TSF file. |
Testsite information[edit]
An radiated emission test, requires that a testsite is used that can have the following components.
Spectrum analyser | Devices 2 | |
Pre amplifier | Devices 2 | |
Antenna | Devices 1 | |
Turn table | Devices 1 | |
Antennatower | Devices 1 | |
Cables | ||
1 | Cable preamp -> analyser | Cables |
2 | Cable antenna -> preamp | Cables |
Note: | Usage of cable correction factors is not mandatory. However, using cable correction factors will increase measurement accuracy during emission measurements. When in doubt contact your reseller. |
Multiband[edit]
The radiated emission Multiband test, is a very flexible and powerful test to perform radiated emission tests. When the multiband test is performed, it will first perform a prescan measurement on all the specified locations. After this prescan is finished the temporary results are shown, and some peaks are automatically detected and shown. At this moment those peaks are NOT measured yet with the final measurement detectors and are also not optimized yet. The end-user now has the possibility to add additional peaks, or do some other peak investigation/changes. When the end-user is satisfied with the list of detected peaks, he can continue with the final measurement, by pressing the Automatic button again. When the end-user has configured peak optimization to be active, the peak optimization will now also be performed. Now the peaks will be measured with the detector that are selected in the Final peak measurement box. Only after those measurements are finalized, those detector values will become available in the list of detected peaks.
The test engineer can configure a complete radiated emission test in the Radiated Emission configuration menu. The test engineer can change the frequency range from one frequency band or the RBW of several bands. It all depends on the selection of bands. When several bands are selected and some options are blank, this means that these settings in bands are different. For example if the test engineer selects both frequency band in the window above, the frequency range will be blank. If the engineer sets the start and stop frequency, all the selected bands will have the same frequency setting. One of the advantages of this feature is the quick settings of several settings like the RBW or the peak detection.
Frequency window[edit]
Turntable window[edit]
Start Angle | Sets the start position of the turntable. |
End Angle | Sets the stop position of the turntable. |
Steps | Sets the number of steps for one turntable rotation. |
Turn during measurements | This will force the turntable to continuously rotate during the test and will disable steps setting. |
EUT angle offset | The offset of the EUT compared to the zero angle of the table. |
Optimize Angle | Optimized settings for searching the correct angle. |
Area | Range over which the peak search will be performed (0 to 360 degrees max.). |
Step size | The angle step size. |
Antenna tower window[edit]
Max. height | Sets maximum height of the antenna tower. |
Min. height | Sets the minimum height of the antenna tower. |
Steps | Sets the number of steps to go from min. height to max. height. |
Move during measurements | This will force the Antenna Tower to continuously move during the test and will disable steps setting. |
Optimize height | The software will automatically detect on which antenna height maximum emission will occur. |
Area | Range over which the peak search will be performed (0 to Max height). |
Step size | The height step size. |
Antenna window[edit]
Polarisation[edit]
- Horizontal
- Vertical
- Both
Distance[edit]
Receiver settings[edit]
Warning: | When older analyzers and receivers are used that switch between measuring in a linear or logarithmic scale during the pre-scan and final-measurement phases, it is advised to not use a fixed reference level |
Traces window[edit]
Detectors | The detector settings (Peak, Average, Quasi-peak, RMS) used during sweeptime. This setting is generic. So it is possible to select multiple detectors, but only one detector can be selected due to the device limitations. In that case for each enabled detector the amount of sweeps will be performed by RadiMation®. |
Number of sweeps | The number op peak hold sweeps for each measurement can be selected. If this value is set to, for example 10, the software will measure the frequency band 10 times for each turntable and antenna tower position. This value will normally be set to 1 for measurement receivers while a higher value is used for spectrum analysers. The amount of required peak sweeps is depending on the type of signal and the setting of the sweep speed. For spectrum analysers and CW signals you can use a relatively low amount of peak sweeps, for example 10. But when you have discontinues signals like a spark bridge, you may need 100 peak sweeps or more. A good indication if you are using enough peak sweeps is to look at the envelope of the frequency spectrum. When it has gaps or jumps then you are not using enough sweeps to determine a correct signal envelope. |
Final peak measurement[edit]
In the final peak measurement window the test engineer can configure the detectors used during the final emission measurements of the detected peaks. The first value is the time constant of the detector while the second value is used for the measure time at each frequency point for this detector. The time constant is send to the receiver, to set the sample time of the detector. To select a detector, check the desired button.
Peak detection window[edit]
No peaks | When no final peak measurements are required select the option no peaks. |
Maximum Peaks | With the max. peaks option, the user can limit the number of peak signals the software will detect and re-measure. |
Test site window[edit]
Limit lines window[edit]
All peaks above “xx” below the limit lines | In the peak detection window, the test engineer can configure which signal peaks must be detected. If the operator selects a value of 5 dB, the software will detect all peaks, which are higher than 5 dB below the limit line. |
Change Order window[edit]
You need to perform a test as shown but you have 2 test sites. One with an antenna with the frequency range that is equal to the total band. The second test site you have 2 antennas, one for every frequency band. For test site one you want the RBW filter to change as little as possible to prevent the old analyser from breaking down.
So for Site 1 you want:
- Band A RBW 9 kHz
- Band B RBW 9 kHz
- Band A RBW 120 kHz
- Band B RBW 120 kHz
And for test site 2:
- Band A RBW 9 kHz
- Band B RBW 9 kHz
- Band A RBW 9 kHz
- Band B RBW 9 kHz
- RBW
- Testsite
- Frequency band
- Band A RBW 9 kHz
- Band B RBW 9 kHz
Note: | If you have any questions regarding the setting of the change order please contact your reseller. |
Manual Mode[edit]
Turn table[edit]
Antenna tower[edit]
Test site[edit]
Final measurement[edit]
Peaks window[edit]
Max Peaks | Maximum allowed amount of peaks to be automatically determined. |
Detect Peaks | Detects the configured amount of sweeps in the measured spectrum. |
Measure Peaks | Measures all selected peaks with the configured settings in the final measurement window. |
Peak Actions | Allows several actions to be performed on the detected peaks, like select all and deselect all.
Delete Peaks | Delete the selected peaks from the list. |
Sweeps | Amount of sweeps to be measured. |
Take Sweeps | Triggers the receiver of analyser to take the configured amount of sweeps. |
Continuous Measure | Start performing of taking measurements. This is a heavy process and it is normal when more CPU is used by the computer. |
Continuous Measure Write | Each new measurement will overwrite the previous measurement data. |
Continuous Measure Max-hold | Only higher new measurement values will overwrite the previous measurement data. |
Clear measurement data | Removes all previous measurement data. |
Anechoic chamber[edit]
Stop | Sets stop frequency |
Start position | Sets the start angle of the turntable. |
Stop position | Sets the stop angle of the turntable. |
# | Number of locations from Start postion to Stop position that should be measured. |
Peak search | The software will automatically detect on which turntable angle the maximum measurement value of each peak is present. |
Area | Range over which the peak search will be performed. The initially detected turntable angle of the peak will be the middle of this Area, and the total search area for this peak will be half of this area clockwise and half of this area counter-clockwise. |
Step size | The step size for each turntable movement. |
Threshold | This value is only used during the Intelligent mode. It influences how long the movement is continued. The movement will stop when the measurement value is lower than the specified Threshold below the highest known measurement value of the searched peak. |
Mode | The mode setting determines the way a peak is detected. The following modes are available:
Intelligent[edit]
In this mode the software increases the angle of the turntable from the initial point with a step equal to Step size as long as the measurement value is not more than Threshold below the already known maximum measurement value. As soon as measurement value is detected that is Threshold below the already known meaximum value, the turntable movement is reversed until the initial point and from this initial point the angle of the turntable is decreased with a step equal to Step size until a measurement value is measured that is Threshold below the already known maximum measurement value. The step on which the highest measurement value is measured, will be the optimum peak search location that is found for that peak.
Warning: | This might cause a measurement error if the intial number of steps (#) is set to a low value. |
Complete area[edit]
Warning: | This might cause a measurement error if the Area is set to a smaller value than the original stepsize (given by the stop position minus start position divided by the number of steps). |
# | Number op locations from Max. height to Min. height that should be measured. |
Peak search | The software will automatically detect on which antenna height the maximum measurement value of each peak is present. |
Area | Range over which the peak search will be performed. The initially detected antenna height of the peak will be the middle of this Area, and the total search area for this peak will be half of this area up and half of this area down. |
Step size | The step size for each antenna height movement. |
Intelligent[edit]
In this mode the software increases the height of the antenna from the initial point with a step equal to Step size as long as the measurement value is not more than Threshold below the already known maximum measurement value. As soon as measurement value is detected that is Threshold below the already known meaximum value, the antenna movement is reversed until the initial point and from this initial point the distance of the clamp is decreased with a step equal to Step size until a measurement value is measured that is Threshold below the already known maximum measurement value. The step on which the highest measurement value is measured, will be the optimum peak search location that is found for that peak.
Complete area[edit]
Polarisation[edit]
- Horizontal
- Vertical
- Both
Distance[edit]
Warning: | All these settings are generic. Therefore, always verify that the configured settings are also supported by the used hardware to ensure it is correctly used and no measurement faults are introduced. Use a fixed value to disabled interference of equipment intelligence. |
Max. hold measurements[edit]
Traces window[edit]
Detectors window[edit]
Test options window[edit]
Record data | In the test options window the operator can select whether all RAW data must be stored or only the measurement results are stored. It should be noted that for full tracebility, all test data should be stored. |
Narrow band / broad band discrimination | RadiMation® supports two types of narrow band / broad band determination. |
Limits | Distortion type |
Loading a TSF file
Test Procedure[edit]
Info screen[edit]
Settings | In the settings window all the used settings are displayed. |
Graph control | In the graph control window the scale of the graph can be changed. You can show or hide the table by selecting or deselecting the show table checkbox. |
Trace | In the trace window you can control the traces that are shown in the graph by selecting or deselecting the checkbox. If during a measurement a trace is not used then the check box is grayed out. |
Detector | The detector window gives you the possibility to show and hide the values measured on the peaks. If during a measurement a type of detector is not used for determining the value on the peak the checkbox is grayed out. |
Table | In the table all the measured peaks are showed. The table also shows the limit values for that frequency point when a limit was given at the beginning of the test. |
Test site information[edit]
Cables | ||
1 | cable Preamp -> analyser | Cables |
2 | cable Antenna -> Preamp | Cables |
Note: | Usage of cable correction factors is not mandatory. However, using correction factors will increase measurement accuracy during emission measurements.
Fixed height[edit]
Intelligent[edit]
Complete area[edit]
Intelligent[edit]
Complete area[edit]
Polarisation[edit]
- Horizontal
- Vertical
- Both
Distance[edit]
Traces window[edit]
Max. Peaks | With the ‘max. peaks” option, the user can limit the number of peak signals the software will detect and re-measure. |
Loading a TSF file
Pre amplifier | Devices2 | |
Cables | ||
1 | cable amplifier ->Spectrum | Cables |
2 | cable antenna ->Preamp | Cables |
GTEM[edit]
Correlation method[edit]
Measurement procedure[edit]
- Tests
- Radiated emission
- G-TEM
- Radiated emission
- Tests
Test configuration[edit]
OATS settings[edit]
G-TEM settings[edit]
Traces window[edit]
Max. Peaks
Starting a G-TEM test[edit]
Cables | ||
1 | cable Preamp->analyser | Cables |
2 | cable Antenna->Preamp | Cables |
Reference | Sets the reference level of the receiver |
RBW | Sets the Resoution Band Width filter |
Data correction[edit]
[edit]
Traces Menu[edit]
Traces[edit]
Detectors[edit]
- Peak detector
- Average detector
- Quasi peak detector
- RMS detector
Zoom function[edit]
X-axis | When this option is switched on, the frequency settings of the receiver and the graph will be automatically adjusted when the user zooms in to the graph. |
Y-axis | When this option is switched on, the amplitude settings of the receiver and the graph will be automatically adjusted when the user zooms in to the graph. |
Limit lines[edit]
[edit]
Merge[edit]
X + k * S[edit]