| Line 249: | Line 249: | ||
===Info screen=== | ===Info screen=== | ||
Note | {{Note|The pass/fail criteria, shown in the tables do not take the measure uncertainty of the test setup into account.}} | ||
You can access the info screen by selecting the test you whish to see and then press the info button. | You can access the info screen by selecting the test you whish to see and then press the info button. | ||
Revision as of 09:28, 30 August 2008
Radiated emission[edit]
The RadiMation® package support three main radiated emission methods: • Anechoic chamber method • Fixed height method • G-TEM method
Anechoic chamber[edit]
Frequency window[edit]
Start : Sets start frequency Stop : Sets stop frequency
Turntable window[edit]
Start position : Sets the start angle of the turntable. Stop position : Sets the stop angle of the turntable.
- : Sets the number of steps for one turntable rotation.
Peak search : The software will automatically detect on which angle maximum emission will occur.
Area : Range over which the peak search will be performed (0 to 360 degrees max.). Step size : The angle step size. Threshold : This value determines the acceptance criteria for a peak. Mode : The mode setting determines the way a peak is detected. The following modes are available: - Intelligent - Complete area Intelligent
Remark: This might cause a measurement error if the number of steps is set to a low value.
Complete area
Remark: This might cause a measurement error if the “Area” is set to a low value relative to the area given by the stop position minus start position dived by number of steps.
Antenna tower window[edit]
Max. height : Sets maximum height of the antenna tower. Min. height : Sets the minimum height of the antenna tower.
- : Sets the number of steps to go from min. height to max. height.
Peak search : The software will automatically detect on which antenna height maximum emission will occur.
Area : Range over which the peak search will be performed (0 to n meter). Step size : The distance for each step. Threshold : This value determines the acceptance criteria for a peak Mode : The mode setting determines the way a peak is detected. The following modes are available - Intelligent - Complete area Intelligent
Complete area
Remark: This might cause a measurement error if the “Area” is set to a low value relative to the area given by the max. height minus min. height dived by number of steps.
Antenna window[edit]
Polarisation
- Horizontal
- Vertical
- Both
Distance
RadiMation uses the distance information for reference only.
Receiver settings[edit]
Reference level : Sets the reference level of the receiver Attenuator : Sets the receiver attenuator level RBW : Sets the Resolution BandWidth filter VBW : Sets the Video BandWidth filter Sweep : Sets the sweep time of the receiver Pre-amp : Sets the pre-amp gain Step frequency : Sets the frequency step size of the receiver Measure time : Sets the measure time of the receiver
Max. hold measurements[edit]
Traces window[edit]
Detectors window[edit]
Peak detection window[edit]
In the peak detection window, the test engineer can configure which signal peaks must be detected. If the operator selects a value of 6 dB, the software will detect all peaks, which are higher than 6 dB below the limit line.
Max. Peaks[edit]
With the max. peaks option, the user can limit the number of peak signals the software will detect and re-measure.
Test site window[edit]
Test equipment
In the test site window the test engineer can select which equipment list will be used during this test.
Test engineer
In the test engineer window, the test engineer can select its own name. The test engineer name will be stored by the test results.
Equipment icon
By clicking on the equipment icon, the equipment list can be viewed and edited.
Limit lines window[edit]
Test options window[edit]
Record data
Narrow band / broad band discrimination
Radimation supports two types of narrow band / broad band determination. The first one is called “Generic”. During the determination of the peak, the so called ‘zooming’. Radimation verifies if the peak is bigger or equal to twice the RBW filter. If so, the peak is determined broad band. Otherwise it is called narrow band. The second method is called “Mil Standard”. This method is also based on the RBW filter. But now the filter is changed to determine the type of peak. First the peak is measured with the current RBW, then it is made 10 times bigger. If multiplying the current RBW gives a RBW that is bigger then 1 MHz the current RBW is divided by 10. A delta RBW is calculated according to the formula below.
Delta RBW = 10log(RBW1 / RBW2)
Delta V = V1 – V2
Limits Distortion type Delta V <= 5 Delta RBW Narrow band Delta V is > than 5 Delta RBW and delta V is <= 15 delta RBW Random noise Delta V > 15 delta RBW Broad band
Loading a TSF file
Test Procedure[edit]
Radimation now performs a maxhold on all the sweeps and determines the peaks. Then it determines the position a peak was found. And changes the turntable and antenna to that current position to re-measure the peak. When multiple peaks have been detected, the most compact way is determined to measure these peaks.
Info screen[edit]
Settings
In the settings window all the used settings are displayed.
Graph control
In the graph control window the scale of the graph can be changed. You can show or hide the table by selecting or deselecting the show table checkbox.
Trace
In the trace window you can control the traces that are shown in the graph by selecting or deselecting the checkbox. If during a measurement a trace is not used then the check box is grayed out. Detector
The detector window gives you the possibility to show and hide the values measured on the peaks. If during a measurement a type of detector is not used for determining the value on the peak the checkbox is grayed out.
Table
In the table all the measured peaks are showed. The table also shows the limit values for that frequency point when a limit was given at the beginning of the test.
Test site information[edit]
Device name Tab in Radimation configuration window Spectrum analyser Standard 2 Pre amplifier Standard 2 Antenna Standard 1
Cables
1 Pre amp->Spectrum Cables 2 Ant->Pre amp Cables
Note: Usage of cable correction factors is not mendatory. However, using correction factors will increase measurement accuraccy during emission measurements. When in doubt contact your reseller.
Fixed height test method[edit]
In the turn table window, the following parameters can be configured:
Intelligent
Complete area
Max. height : Sets maximum height of the antenna tower. Min. Height : Sets the minimum height of the antenna tower.
Intelligent
Complete area
Polarisation
- Horizontal
- Vertical
- Both
Distance
In this box, the operator can enter the distance between antenna and EUT. RadiMation uses the distance information for reference only.
Traces window[edit]
Max. Peaks
With the ‘max. peaks” option, the user can limit the number of peak signals the software will detect and re-measure.
Test equipment
Test engineer
Equipment icon
Loading a TSF file
Radimation now performs a maxhold on all the sweeps and determines the peaks. Then it determines the position a peak was found. The turntable position is changes to that position to re-measure the peak. The antenna tower is changed in height according to the settings.
Cables
Note:
measurements.
G-TEM Method[edit]
Correlation method[edit]
Ptr2 = X2 + Y2 + Z2
Measurement procedure[edit]
“Tests> Radiated emission > G-TEM”.
Test configuration[edit]
Frequency range selection
Frequency list selection
OATS settings
G-TEM settings
Receiver settings
Traces window
Detectors window
Max. Peaks
Test equipment
Test engineer
Equipment icon
Starting a G-TEM test[edit]
Loading a TSF file
Cables
Manual mode[edit]
Start : Sets start frequency Stop : Sets stop frequency Reference : Sets the reference level of the receiver Attenuator : Sets the receiver attenuator level RBW : Sets the Resoution Band Width filter VBW : Sets the Video BandWidth filter Sweep : Sets the sweep time of the receiver Pre-amp : Sets the pre-amp gain
The figure on the next page shows the receiver settings menu.
Data correction
[edit]
Search peak
RadiMation can detect peaks automatically. From the “peaks” TAB, choose “Search peak” to detect the maximum signal. The software will measure the detected peak.
Add peak
The measured values can be added to the peak list by pressing the “Add Peak” button.
Search angle
By pressing the “Search Angle” button, the software starts a turntable scan to determine at which turn table angle maximum emission takes place.
Search Height
By pressing the “Search Height” button, the software starts an antenna height scan to determine at which antenna height maximum emission takes place.
Traces Menu[edit]
Traces
Detectors
- Peak detector - Average detector - Quasi peak detector - RMS detector
Turntable and antenna tower position
Zoom function
Limit lines[edit]
[edit]
Merge function[edit]
X+k*S Calculations[edit]
Anechoic chamber (Multi band)[edit]
Start position : Sets the start angle of the turntable. Stop position : Sets the stop angle of the turntable. Steps : Sets the number of steps for one turntable rotation. EUT angle offset : The offset of the EUT compared to the zero angle of the table Optimize Angle : Optimized settings for searching the correct angle.
The area is defined 50% left of the starting position and 50% right. So if the area is 30 degrees, RadiMation will scan between starting position plus and minus 15 degrees.
Max. height : Sets maximum height of the antenna tower. Min. height : Sets the minimum height of the antenna tower. Steps : Sets the number of steps to go from min. height to max. height. Optimize height : The software will automatically detect on which antenna height maximum emission will occur.
Area : Range over which the peak search will be performed (0 to Max height). Step size : The height step size.
The area is defined 50% above of the starting position and 50% below. So if the area is 1 meter, RadiMation will scan between starting position plus and minus 50 cm.
Polarisation
- Horizontal
- Vertical
- Both
Distance
Reference level : Sets the reference level of the receiver Attenuator : Sets the receiver attenuator level RBW : Sets the Resolution Band Width filter VBW : Sets the Video Band Width filter Sweep : Sets the sweep time of the receiver Step frequency : Sets the frequency step size of the receiver Measure time : Sets the measure time of the receiver Pre-amp : Sets the pre-amp gain
Traces window[edit]
Number of sweeps
The number op peak hold sweeps for each measurement can be selected. If this value is set to, for example 10, the software will measure the frequency band 10 times for each turntable and antenna tower position. This value will normally be set to 1 for measurement receivers while a higher value is used for spectrum analysers. The amount of required peak sweeps is depending on the type of signal and the setting of the sweep speed. For spectrum analysers and CW signals you can use a relatively low amount of peak sweeps, for example 10. But when you have discontinues signals like a spark bridge, you may need 100 peak sweeps or more. A good indication if you are using enough peak sweeps is to look at the envelope of the frequency spectrum. When it has gaps or jumps then you are not using enough sweeps to determine a correct signal envelope.
Final peak measurement[edit]
No peaks
When no final peak measurements are required select the option no peaks
Max. Peaks
Test equipment
In the test site window the test engineer can select which equipment list will be used during this test. It is possible to use different test equipment for every configured frequency band.
Equipment icon
Change Order window[edit]
So for Site 1 you want:
- Band A RBW 9 kHz
- Band B RBW 9 kHz
- Band A RBW 120 kHz
- Band B RBW 120 kHz
And for test site 2:
- Band A RBW 9 kHz
- Band B RBW 9 kHz
- Band A RBW 9 kHz
- Band B RBW 9 kHz
- RBW
- Testsite
- Frequency band
- Band A RBW 9 kHz
- Band B RBW 9 kHz
Note: If you have any questions regarding the setting of the change order please contact your reseller.
Loading a TSF file
Info screen[edit]
Note : The pass/fail criteria, shown in the tables do not take the measure uncertainty of the test setup into account.
You can access the info screen by selecting the test you whish to see and then press the info button. The window appearing looks a lot like the manual mode screen, the reason that it looks the same is because it is. You can continue testing after you finished a test, just select the test site you want to use and you can continue testing. Note: continuing the test is only possible with the selected test site. RadiMation will not select the correct test site for you. All measurements are done with the selected test site. If you want automatic changes of the test site, restart the configured TSF file.
Cables
Manual Mode (Multi band)
Turn table[edit]
Antenna tower[edit]
Test site[edit]
Before manual mode can be used the test site needs to be selected so that Radimation® knows which devices to use.
Final measurement[edit]
Peaks window[edit]
Take sweeps
Triggers the receiver of analyzer to take the configured amount of sweeps
Detect peaks
Detects the configured amount of sweeps in the measured spectrum
Measure Peaks
Measures all selected peaks with the configured settings in the final measurement window
Delete Peaks
Delete the selected peaks from the list.
Peak actions
Allows several actions to be performed on the detected peaks, like select all and deselect all