| Line 64: | Line 64: | ||
{{ScreenElementDescription|GPIB Delay|GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast pc’s (>2.5 GHz). This is most of the time noticeable when a driver is sometimes working and some times gives a GPIB(EABO or TIMO) error. These problems are mostly random. If this is your problem insert a GPIB delay time of 3000. Run the test again and see of the problem as disappeared. Is the problem has disappear then your problem was timing, if not please contact your reseller and report the problems you are having.}} | {{ScreenElementDescription|GPIB Delay|GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast pc’s (>2.5 GHz). This is most of the time noticeable when a driver is sometimes working and some times gives a GPIB(EABO or TIMO) error. These problems are mostly random. If this is your problem insert a GPIB delay time of 3000. Run the test again and see of the problem as disappeared. Is the problem has disappear then your problem was timing, if not please contact your reseller and report the problems you are having.}} | ||
==General Settings== | |||
General settings are settings that can be configured in every device driver. The picture below shows the setting of a signal generator. | General settings are settings that can be configured in every device driver. The picture below shows the setting of a signal generator. | ||
Revision as of 13:19, 19 September 2008
Device drivers[edit]
Device drivers are the lowest layer in Radimation, they make it possible to communicate with thousands of different devices. They make the system flexible, while the Core stays generic. The Core does not even know which device it is controlling, only the type of device. So if you have bought a new spectrum analyser or signal generator you only have to tell the software to use this new device and all the rest stays the same.
Configurable device drivers vs. non configurable device drivers[edit]
Radimation has two types of device drivers, configurable and none configurable device drivers. Configurable devices for instance are powermeter, signal generators and spectrum analysers. For these devices you can set the IEEE address or the serial port which Radimation has to use to be able to communicate with these devices. None configurable devices are couplers and calibration jigs. You might think that it is useless to have non-configurable drivers, but the opposite has been proven many times. Non-configurable drivers still contain important information like the start and stop frequency of a device. With this information Radimation can prevent the test engineer from making large mistakes, like using the wrong coupler in a certain frequency range.
You can configure a device in the configuration screen. You can access the configuration screen by selecting
configuration
configuration
in the main menu. The window showed below will appear.
You can select the type of device you want in the box that is situated top right. The big window will display all currently configured device drivers, like in the picture all configured AD Converters.
New[edit]
If you press New a new window will appear, like the one below. Select the device you want and press New, if you do not whish to create a new device press Close.
If you select New the window below will appear. You can now give the device a unique name, which will be used in the software.
Edit[edit]
To edit the configuration of a device, select the device in the list and press Edit. Now two things can happen, either you seen an configuration screen of the device or an message box that tells you that you can not configure this device. The message box is explained in the chapter Messages and the configuration screen is explained in the chapter Device specific configuration
Remove[edit]
If you want to remove a device driver, select the device and press Remove. Please note that this driver will then not be available in the test sites, not even if you insert the exact same type of device with the exact the same name.
RS 232 Setting[edit]
In the textbox you can type the COM port which Radimation has to use to able to communicate with the device. Baudrate, 7 or 8 bits and parity do not need to set because this is device specific.
IEEE Setting Basic[edit]
| The primary address specifies the address of the device, so if the device you want to configure is on address is on 20 you enter 20. Please consult the manual of the device how to get the GPIB address of the device. |
| Advanced configuration enables the user to setup the GPIB board. The configuration is discussed in “IEEE settings advanced” This option should only be used if the default settings are not sufficient enough. |
IEEE Setting advanced[edit]
| The second address is default 0, and should only be changed when needed. For further information please look in the help of National Instruments 488.2. |
| GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast pc’s (>2.5 GHz). This is most of the time noticeable when a driver is sometimes working and some times gives a GPIB(EABO or TIMO) error. These problems are mostly random. If this is your problem insert a GPIB delay time of 3000. Run the test again and see of the problem as disappeared. Is the problem has disappear then your problem was timing, if not please contact your reseller and report the problems you are having. |
General Settings[edit]
Description[edit]
In the description window the description of the device can be changed/viewed. The description can be used in the report generator. Changing the description does not result in losing the device in the test sites. the description is automatically updated in test site. When generating a report with a test prior to the change the old description is inserted. 15.3.8 Brand
In the brand window the brand of the device can be changed/viewed. This brand can be used in the report generator.
Type[edit]
In the type window the brand of the device can be changed/viewed. This type can be used in the report generator.
ID[edit]
In the ID window the internally used ID of the device can be changed/viewed. This ID can be used in the report generator. The main function of this window is to link your measurement to your devices for easier reproduction.
Serial number[edit]
Hardware version[edit]
In the hardware version the brand of the device can be changed/viewed. This brand can be used in the report generator.
Software version[edit]
In the software version the brand of the device can be changed/viewed. This brand can be used in the report generator.
Calibration Expires[edit]
You can set the date that this device needs to be calibrated. Depending upon the setting in the configuration window Radimation will use this date. When you press the control a small window will appear, allowing you to select the new date.
Advanced[edit]
Pressing advanced opens the advanced menu of the device driver. Device specific configuration will explain this menu for every device type. Please note that the configuration does not apply on the configurable or virtual drivers. Please view chapter Configurable devices or Virtual devices for these devices.
Signal generator[edit]
Pressing advanced will open an IEEE configuration screen. Please view chapter IEEE setting for a complete description. See chapter 14.2 and 14.3 for correcting this device.
Amplifier[edit]
When an amplifier can be remotely controlled the specific window will appear. Please view chapter IEEE or RS232 setting for a complete description. When the amplifier can not be remotely controlled the message This Device cannot be configured will appear. See chapter 14.2 and 14.3 for correcting and protecting this device.
Antenna[edit]
When pressing advanced the message This Device cannot be configured will appear because this device can not be controlled remotely. See chapter 14.2 and 14.3 for correcting this device.
Coupler[edit]
Powermeter[edit]
Wait Time: Wait time is the time that Radimation may take for one measurement
Max Difference: The maximum allowed difference between the minimum and the maximum of measurements defined in the measurement window
Measure: Measure is the minimum amount of measurements Radimation has to make to determine the power.
Max Measure: Maximum measurement is the maximum amount of measurement Radimation may take to determine the power.
Now that all windows have been generally explained, the procedure Radimation uses is the following. Radimation takes the amount of measurements as defined in the Measure window. After that Radimation determines the minimum, maximum and difference. When the difference is equal or smaller then defined in Max difference Radimation determines the power. If the difference is greater then defined, Radimation takes one new measurement. Replaces the oldest value with the new one. Determines the minimum, maximum and difference again. This continues as long as the difference is larger then defined and the maximum amount of measurement has not yet been reached. If the maximum amount of measurement has been reached the last measurement is taken as the measured value.
Some notes:
Speed up(1): Sometimes slower means faster. For instance, if you have a slower powermeter (resistor head) it may be quicker to have a longer waiting time. Because the powermeter has more time to determine the right value, Radimation needs less measurements to determine the value. It is up to the engineer to find the right accuracy vs. time setting.
Measuring: Powermeter who doesn't have a RMS detector, should not be used in Fast constant mode.
Field Sensor[edit]
Measure: Measure is the minimum amount of measurements Radimation has to make to determine the field.
Max Measure: Maximum measurement is the maximum amount of measurement Radimation may take to determine the field.
Advanced: Opens the advanced menu, this can be RS 232, IEEE or device specific settings like Range mode.
Now that all windows and buttons have been generally explained, the procedure Radimation uses is the following. Radimation takes the amount of measurements as defined in the Measure window. After that Radimation determines the minimum, maximum and difference. When the difference is equal or smaller then defined in Max difference Radimation determines the field. If the difference is greater then defined, Radimation takes one new measurement. Replaces the oldest value with the new one. Determines the minimum, maximum and difference again. This continues as long as the difference is larger then defined and the maximum amount of measurement has not yet been reached. If the maximum amount of measurement has been reached the last measurement is taken as the measured value.
Speed up: Sometimes slower means faster. For instance, if you have a slower field sensor it may be quicker to have a longer waiting time. Because the field sensor has more time to determine the right value, Radimation needs less measurements to determine the value. It is up to the engineer to find the right accuracy vs. time setting.
AD converter[edit]
Injection device[edit]
Calibration Jigs[edit]
Current Sensor[edit]
Pre Amplifiers[edit]
LISN[edit]
When an LISN can be remotely controlled the specific window will appear. Please view chapter IEEE or RS232 setting for a complete description. When the LISN can not be remotely controlled the message This Device cannot be configured will appear. See chapter 14.2 and 14.3 for correcting this device.
Turn Table[edit]
Antenna Tower[edit]
Absorbing Clamps[edit]
Clamp positioner[edit]
Cables[edit]
Switch matrix[edit]
EUT Controller[edit]
Virtual devices[edit]
Virtual devices are devices that act like normal devices but do not really exist. If you create a test site with only virtual devices, you can perform complete virtual tests. You might wonder why Radimation supports virtual device drivers. It is mainly used for debugging and solving software problems, but is has proven to be very useful when used as a temporarily workaround. For example a test site has an amplifier that is IEEE controlled and one day somebody accidentally destroys the communication between computer and amplifier. The test engineer has to perform some tests, he switches the driver for the amplifier for a virtual one. Sets the amplifier in operate by hand and was able to perform the tests that day. When the communication was repaired he changed the driver back again
Configurable devices[edit]
- Press the “New” button.
- Press the “Edit” button.
Remark: Passive equipment such as antenna’s, current probes, cables etc. do also need a device driver. The reason for this is that RadiMation® has to know a number of parameters of these devices. Among others the following information is relevant:
- Frequency range
- Maximum input power
- The report generator needs to know which equipment is used during a test
- Correction files for these devices
Generic settings[edit]
Start and stop frequency
The most generic setting is the start and stop frequency. The default value for the start frequency is 1Hz and for the stop frequency is 40 GHz. The creator of the device is encouraged to set the right start and stop frequency. If the start and stop frequency are set correctly Radimation can warn the test engineer when he/she want to use the device out of its valid frequency range.
Reset
Init
In the init window you need to specify the string that the software needs to send when it want to Init the device. For example *RST is commonly used reset string.
Get ID
In the Get ID window you need to specify the string that the software needs to send when it want to get the ID string of the device. For example *IDN? is commonly used Get ID string. Returned ID
Set Frequency
Set Frequency is the string that needs to send to set the signal generator frequency. The unit is in MHZ, so the string should be made for MHz.
Example: “FRQ__freq__MHZ”.
__freq__ will be replaced by the value that Radimation want to set the signal generator to. The “__” of “__freq__” are two “_”.
Set Carrier
Set Carrier is the string that needs to send to set the signal generator carrierlevel. The unit is in dBm, so the string should be made for dBM.
__carrier__ will be replaced by the value that Radimation want to set the signal generator to. The “__” of “__carrier__ ” are two “_”.
Carrier on
Carrier on is the string that needs to send to set the signal generator carrier on.
Example: “OUTPUT ON”.
Carrier off
Carrier off is the string that needs to send to set the signal generator carrier off.
Example: “OUTPUT OFF”.
AM on
AM on is the string that needs to send to set the internal AM generator of the signal generator. The unit of frequency is KHz and the unit of Modulation Depth is %.
Example: “SOURCE2:FREQ __freq__ KHZ;SOURCE:AM:DEPTH __depth__
PCT;SOURCE:AM:STATE ON”.
AM off
AM off is the string that needs to send to set the internal am modulation of the signal generator off.
External on
External on is the string that needs to send to set the modulator to the external input.
External off
External off is the string that needs to send to set the modulator to the internal input.
PM on
PM on is the string that needs to send to set the internal PM generator of the signal generator. The unit of frequency is KHz and the unit of duty cycle is %.
Example: “SOURCE2:FREQ __freq__ KHZ;SOURCE:PM:DUTY __duty__
PCT;SOURCE:PM:STATE ON”.
PM off
PM off is the string that needs to send to set the internal PM modulation of the signal generator off.
Sine Wave
Sine wave is the string that needs to be send when Radimation wants to set the wave form of the internal source to sine
Example: “SOURCE2:FUNC SIN”
Square Wave
Square wave is the string that needs to be send when Radimation wants to set the wave form of the internal source to square.
Example: “SOURCE2:FUNC SQU”
Amplifier[edit]
Antenna[edit]
Only the start and stop frequency can be set for the amplifier. Chapter generic settings will give more information about the start and stop frequency Coupler
Powermeter[edit]
Set frequency
Set Frequency is the string that needs to send to set the powermeter frequency. The unit is in MHz, so the string should be made for MHz.
__freq__ will be replaced by the value that Radimation want to set the powermeter too. The “__” of “__freq__” are two “_”. Select Channel
Set Select Channel is the string that Radimation needs to send to set the powermeter channel. This is only necessary when the powermeter has more the one channel.
Example: “P1,U1”.
Trigger
Trigger is the string that Radimation needs to send to trigger the powermeter.
Example: “X1”
Result Format
Result Format is the string that Radimation needs to use to decode the value from the string send by the powermeter. The return value is interpreted in dBm
Example: “__result__”
__result__ will be replaced by the value that Radimation get from the powermeter. The “__” of “__result__” are two “_”.
Start Zero
Start Zero is the string that Radimation needs to send to start zeroing the powermeter.
Example: “O1”
Duration
Duration is the time that Radimation waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable result.
Field Sensor
AD converter[edit]
Currently unavailable.
LISN[edit]
Turn Table[edit]
Antenna Tower[edit]
Cables[edit]
Switch matrix[edit]
Messages[edit]
Unknown Device Driver[edit]
This message box is displayed when Radimation is trying to locate a device driver and was unable to find it. If you see this message please contact your reseller and tell him which driver you are trying to use. The reseller will take action so that you will receive the right device driver.
This message box is displayed when Radimation is unable to connect to a device when using GPIB. Please check the cable and the GPIB device driver address setting.
Device not connected[edit]
This message box is displayed when Radimation is unable to connect to the device. Please check cables and device driver settings.
How to make a buscapture[edit]
Please verify your settings with the picture showed above and press OK. Now start capturing by pressing the blue arrow pointing to the right. Start Radimation, and perform the test you need to capture. After the test is done, press the button with the red circle. Then select File and then save as to save to hard disk.
Ddlogger.dat[edit]
Ddlogger.dat is an output file for a debugging tool used by the software engineers at D.A.R.E!!. The tool is extremely useful for remote problem solving. The general idea is quite simple yet really helpful. Radimation inserts all the communication messages with devices in this file. So the software engineer can see what the software is sending and receiving when it communicates with the devices. With this information the engineer is more capable of reproducing/solving the problem, sometimes in combination with a buscapture. Do you need to install some additional software for this functionality? The answer is no, the tool is integrated in Radimation. But how do I turn it on or off? At startup Radimation looks for the ddlogger.dat file in the root of the drive. When it finds the file it will turn on the debugging tool, otherwise the debugging tool is turned off. What are the consequences for the performance? When the debugging tool is turned on, there is a small performance loss because there is additional writing to the harddisk. Therefore the default should be to run Radimation with the debugging tool turned off.
Step by step procedure
- Make sure Radimation is not running.
- Insert an empty text file in the root of the drive and rename it to “ddlogger.dat”. Make sure that the extension (“.txt”) is also changed.
- Start Radimation, during the start the following screen will appear.
- Select no.
- Perform the measurement you have problems with.
- Close Radimation.
- Send the ddlogger.dat file to D.A.R.E!!, preferably in a compressed file format (Zip)
- Remove the ddlogger.dat file from your harddrive.
AD convertors[edit]
Type of communication: IEEE.
Channels 1:
Hewlett Packard 34401A[edit]
Channel 1
Type of measurement: AC Volt Minimum value: 0Volt Maximum value: 1 kVolt.
Channel 2:
Type of measurement: AC Current Minimum value: 0 Amp. Maximum value: 3 Amp.
Channel 3
Type of measurement: DC Volt Minimum value: 0Volt Maximum value: 750 Volt (rms).
Channel 4:
Type of measurement: DC Current Minimum value: 0 Amp. Maximum value: 3 Amp. (rms)
Channel 5
Type of measurement: Resistance (Ohm) Minimum value: 0 Ohm Maximum value: 100 M Ohm
Channel 6
Type of measurement: Frequency Minimum value: 0 Hz. Maximum value: 300 kHz
Channel 7 and 8
Not used
Hewlett Packard 54600[edit]
Channel 1
Type of measurement: V Max. Minimum value: 0Volt Maximum value: 1000 Volt.
Channel 2:
Type of measurement: V Min Minimum value: 0 Volt. Maximum value: 1000 Volt.
Channel 3
Type of measurement: V Average Minimum value: 0Volt Maximum value: 1000 Volt.
Channel 4:
Type of measurement: VPP (peak-peak) Minimum value: 0 Volt. Maximum value: 1000 Volt.
Channel 5
Type of measurement: Frequency Minimum value: 0 Hz Maximum value: 100 kHz
Channel 6
Type of measurement: Period Minimum value: 0 ms Maximum value: 10000 ms
Channel 7
Type of measurement: Rise Time Minimum value: 0 ms Maximum value: 10000 ms
Channel 8
Type of measurement: Fall Time Minimum value: 0 ms Maximum value: 10000 ms
Hewlett Packard 3562A[edit]
Type of communication: GPIB
Channels
Minimum value: 0 dB Maximum value: 100 dB
Hewlett Packard 59313[edit]
Channel 1
Type of measurement: AD channel 1 Minimum value: 0 Maximum value: 2048
Channel 2:
Type of measurement: AD channel 2 Minimum value: 0 Maximum value: 2048
Channel 3
Type of measurement: AD channel 4 Minimum value: 0 Maximum value: 2048
Channel 4:
Type of measurement: AD channel 8 Minimum value: 0 Maximum value: 2048
Channel 5 to 8
Not used.
Channels
Marconi 2305[edit]
Channel 1
Type of measurement: Frequency Minimum value: 0 Maximum value: 1000 MHz
Channel 2:
Type of measurement: AM modulation or FM frequency Deviation Minimum value: 0 Maximum value: 1000
Channel 3 to 8
Not used.
Fluke 45 AC Current[edit]
Channels
Minimum value: 0 mA Maximum value: 10.000 mA
Fluke 45 DC Current[edit]
Channels
Fluke 45 AC Voltage[edit]
Channels
Minimum value: 0 mV Maximum value: 1.000.000 mV
Fluke 45 DC Voltage[edit]
Channels
Fluke 45 Frequency[edit]
Channels
Minimum value: 0 Hz Maximum value: 1.000.000 Hz
Fluke 45 Resistance[edit]
Channels
Minimum value: 0 Ohm Maximum value: 100.000.000 Ohm
Channel 1
Type of measurement: Minimum value Minimum value: 0Volt Maximum value: 353.55 Volt.
Channel 2:
Type of measurement: Maximum value Minimum value: 0 Volt Maximum value: 353.55 Volt
Channel 3
Type of measurement: Amplitude Minimum value: 0Volt Maximum value: 353.55 Volt
Channel 4:
Type of measurement: Peak to peak Minimum value: 0 Volt Maximum value: 707.1 Volt
Channel 5
Type of measurement: RMS Minimum value: 0 Volt Maximum value: 250 Volt
Channel 6
Type of measurement: Frequency Minimum value: 0 Hz. Maximum value: 200 MHz
Channel 7 and 8
Not used
Fluke 8840A AC Current[edit]
Channels
Fluke 8840A DC Current[edit]
Channels
Minimum value: 0 mA Maximum value: 10.000 mA 15.10.17 Fluke 8840A AC Voltage
Channels
Minimum value: 0 mV Maximum value: 1.000.000 mV 15.10.18 Fluke 8840A DC Voltage
Channels
Channels
Channels
Channels
Minimum value: 0 mV Maximum value: 300.000 mV
Channels
Channels 1 to 4
Channels 5 to 8
Not used
Channels 1 to 4
Channels 5 to 8
Not used
Channels 1 to 4
Channels 5 to 8
Not used
Channels 1 to 4
Channels 5 to 8
Not used
D.A.R.E!! Development Radimate 2 and 3[edit]
Channels 1 to 8
Minimum value: 0 Maximum value: 16383
EPI 575[edit]
Channel 1
Type of measurement: Frequency Minimum value: 0 Hz Maximum value: 10 kHz
Channel 2:
Type of measurement: Frequency Minimum value: 0 Hz. Maximum value: 100 kHz
Channel 3
Type of measurement: Frequency Minimum value: 0 Hz Maximum value: 1 MHz.
Channel 4:
Type of measurement: Frequency Minimum value: 0 Hz. Maximum value: 10 MHz.
Channel 5
Type of measurement: Frequency Minimum value: 0 Hz Maximum value: 100 MHz
Channel 6
Type of measurement: Frequency Minimum value: 0 Hz Maximum value: 1 GHz
Channel 7
Type of measurement: Frequency Minimum value: 0 Hz Maximum value: 10 GHz
Channel 8
Type of measurement: Frequency Minimum value: 0 Hz Maximum value: 100 GHz
Channel 1 to 8
Every channel represents one bit of the 8-bits port. So when bit 4 is changing then you will see this in channel 4.