Difference between revisions of "Chapter 15"
(→IEEE Setting advanced) |
(→Configuration) |
Line 8: | Line 8: | ||
==Configuration== | ==Configuration== | ||
+ | Device drivers are used to let your software know which equipment has to be used and controlled during EMC tests. | ||
+ | In {{RadiMation}}, the device drivers must be configured to customer requirements once. During the configuration of the device driver, information like the IEEE address or RS232 COM-port has to be entered. | ||
You can configure a device in the configuration screen. You can access the configuration screen by selecting: | You can configure a device in the configuration screen. You can access the configuration screen by selecting: | ||
{{Menu|Configuration|Configuration|Device Drivers}} | {{Menu|Configuration|Configuration|Device Drivers}} |
Revision as of 14:17, 7 February 2011
Device drivers
Introduction
Device drivers are the lowest layer in RadiMation®, they make it possible to communicate with thousands of different devices. They make the system flexible, while the Core stays generic. The Core does not even know which device it is controlling, only the type of device. So if you have bought a new spectrum analyser or signal generator you only have to tell the software to use this new device and all the rest stays the same.
Configurable device drivers and non-configurable device drivers
Radimation supports two types of device drivers, configurable and non-configurable device drivers. Configurable devices for instance are powermeter, signal generators and spectrum analysers. For these devices you can set the IEEE address or the serial port which Radimation has to use to be able to communicate with these devices. Non-configurable devices are couplers and calibration jigs. You might think that it is useless to have non-configurable drivers, but the opposite has been proven many times. Non-configurable drivers still contain important information like the start and stop frequency of a device. With this information Radimation can prevent the test engineer from making large mistakes, like using the wrong coupler in a certain frequency range.
In RadiMation®, the device drivers must be configured to customer requirements once. During the configuration of the device driver, information like the IEEE address or RS232 COM-port has to be entered.
You can select the type of device you want in the box that is situated top right. The big window will display all currently configured device drivers, like in the picture all configured Signal Generators.
Device Driver Type | Different types of devices are available in RadiMation®. Only the created device drivers of the type that is selected for Device Driver Type will be shown in the list |
Available Device Drivers | Shows a list of all the available device drivers for the selected Device Driver Type |
New | Creates a new RadiMation® device driver for a specific device. It is only possible to create a new device driver for the selected Device Driver Type. |
The required device driver can be selected from this list. The new device driver will then be created when New button is pressed. At that moment it is possible to use the default name of the device driver, or to change it to another (eg. more specific) name.
If you do not whis to create a new device driver press Close.
General Settings
General settings are settings that can be configured in every device driver. The picture below shows an example.
Software version | In the software version the brand of the device can be changed/viewed. This brand can be used in the report generator. |
Brand | In the brand window the brand of the device can be changed/viewed. This brand can be used in the report generator. |
Hardware version | In the hardware version the brand of the device can be changed/viewed. This brand can be used in the report generator. |
Serial number | In the brand window the brand of the device can be changed/viewed. This brand can be used in the report generator. |
Type | In the type window the brand of the device can be changed/viewed. This type can be used in the report generator. |
Device drivers installation date | Shows the date and time at which the last update of the device drivers has been installed. The contents of this cell cannot be changed |
Device drivers versions | Shows the version number of the last installed device drivers update. The contents of this cell cannot be changed |
Zero Interval | When the Zero interval is activated, it is possible to specify a time period in minutes, in which a device does not need to be rezeroed. For accurate measurements it is necessary that Power Meters and Field Sensors are zero-ed. A zero operation however generally takes several seconds to be completed, and it may be valid for a few hours. To prevent that a device is rezeroed during each test initialization, it is possible to set a zero interval in minutes. When a test is initialized and the device is already zeroed within the specified zero interval, no zero will be performed at that time. Specifying and activating the zero interval, can be a large reduction of the time that is needed to initialize each test.
This setting is only available for powermeter and field strength sensor devices. |
Knowledgebase | Pressing the Knowledgebase button, opens a new web-browser window which will show the Template:RadiWiki page that is specific for that device driver. That Template:RadiWiki page can contain some additional information or a detailed explanation of all advanced settings. |
Device specific configuration
Signal generator
Pressing advanced will open an IEEE configuration screen. Please view chapter IEEE setting for a complete description. See chapter 14.2 and 14.3 for correcting this device.
Amplifier
When an amplifier can be remotely controlled the specific window will appear. Please view chapter IEEE or RS232 setting for a complete description. When the amplifier can not be remotely controlled the message This Device cannot be configured will appear. See chapter 14.2 and 14.3 for correcting and protecting this device.
Antenna
When pressing advanced the message This Device cannot be configured will appear because this device can not be controlled remotely. See chapter 14.2 and 14.3 for correcting this device.
Coupler
Powermeter
Wait Time | Wait time is the time that Radimation may take for one measurement |
Max Difference | The maximum allowed difference between the minimum and the maximum of measurements defined in the measurement window. |
Measure | Measure is the minimum amount of measurements Radimation has to make to determine the power. |
Max Measure | Maximum measurement is the maximum amount of measurement Radimation may take to determine the power. |
Now that all windows have been generally explained, the procedure Radimation uses is the following. Radimation takes the amount of measurements as defined in the Measure window. After that Radimation determines the minimum, maximum and difference. When the difference is equal or smaller then defined in Max difference Radimation determines the power. If the difference is greater then defined, Radimation takes one new measurement. Replaces the oldest value with the new one. Determines the minimum, maximum and difference again. This continues as long as the difference is larger then defined and the maximum amount of measurement has not yet been reached. If the maximum amount of measurement has been reached the last measurement is taken as the measured value.
Field Sensor
Wait Time | Wait time is the time that Radimation may take for one measurement. |
Measure | Measure is the minimum amount of measurements Radimation has to make to determine the field. |
Max Measure | Maximum measurement is the maximum amount of measurement Radimation may take to determine the field. |
Advanced | Opens the advanced menu, this can be RS 232, IEEE or device specific settings like Range mode. |
Now that all windows and buttons have been generally explained, the procedure Radimation uses is the following. Radimation takes the amount of measurements as defined in the Measure window. After that Radimation determines the minimum, maximum and difference. When the difference is equal or smaller then defined in Max difference Radimation determines the field. If the difference is greater then defined, Radimation takes one new measurement. Replaces the oldest value with the new one. Determines the minimum, maximum and difference again. This continues as long as the difference is larger then defined and the maximum amount of measurement has not yet been reached. If the maximum amount of measurement has been reached the last measurement is taken as the measured value.
AD converter
Injection device
Calibration Jigs
Current Sensor
Pre Amplifiers
Receivers / Spectrum analyser
LISN
When an LISN can be remotely controlled the specific window will appear. Please view chapter IEEE or RS232 setting for a complete description. When the LISN can not be remotely controlled the message This Device cannot be configured will appear. See chapter 14.2 and 14.3 for correcting this device.
Turn Table
Antenna Tower
Absorbing Clamps
Clamp positioner
Cables
Switch matrix
EUT Controller
Communication settings
Depending on the brand and model of the device, it may be necessary to specify the parameters for the communication with the device. The IEEE 488 and RS232 buses are most commonly used. This section describes the relevant communication parameters.
RS 232 Setting
In the textbox you can type the COM port which Radimation has to use to able to communicate with the device. Baudrate, 7 or 8 bits and parity do not need to set because this is device specific.
IEEE Setting Basic
Primary Address | The primary address specifies the address of the device, so if the device you want to configure is on address is on 20 you enter 20. Please consult the manual of the device how to get the GPIB address of the device. |
Show advanced configuration | Advanced configuration enables the user to setup the GPIB board. The configuration is discussed in “IEEE settings advanced” This option should only be used if the default settings are not sufficient enough. |
GPIB Board | With GPIB Board you can specify the GPIB board that is used. The default value is 0 and can only be different when multiple GPIB boards are present. |
Secondary Address | The second address is default 0, and should only be changed when needed. For further information please look in the help of National Instruments 488.2. |
GPIB Delay | GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast pc’s (>2.5 GHz). This is most of the time noticeable when a driver is sometimes working and some times gives a GPIB(EABO or TIMO) error. These problems are mostly random. If this is your problem insert a GPIB delay time of 3000. Run the test again and see of the problem as disappeared. Is the problem has disappear then your problem was timing, if not please contact your reseller and report the problems you are having. |
Virtual devices
Virtual devices are devices that act like normal devices but do not really exist. If you create a test site with only virtual devices, you can perform complete virtual tests. You might wonder why Radimation supports virtual device drivers. It is mainly used for debugging and solving software problems, but is has proven to be very useful when used as a temporarily workaround. For example a test site has an amplifier that is IEEE controlled and one day somebody accidentally destroys the communication between computer and amplifier. The test engineer has to perform some tests, he switches the driver for the amplifier for a virtual one. Sets the amplifier in operate by hand and was able to perform the tests that day. When the communication was repaired he changed the driver back again
- Press the “New” button.
- Press the “Edit” button.
- Frequency range
- Maximum input power
- The report generator needs to know which equipment is used during a test
- Correction files for these devices
Generic settings
Start and stop frequency
The most generic setting is the start and stop frequency. The default value for the start frequency is 1Hz and for the stop frequency is 40 GHz. The creator of the device is encouraged to set the right start and stop frequency. If the start and stop frequency are set correctly Radimation can warn the test engineer when he/she want to use the device out of its valid frequency range.
Reset
Init
In the init window you need to specify the string that the software needs to send when it want to Init the device. For example *RST is commonly used reset string.
Get ID
In the Get ID window you need to specify the string that the software needs to send when it want to get the ID string of the device. For example *IDN? is commonly used Get ID string. Returned ID
Signal generator
Set Frequency | Set Frequency is the string that needs to send to set the signal generator frequency. The unit is in MHZ, so the string should be made for MHz. |
Example: “FRQ__freq__MHZ”.
__freq__ will be replaced by the value that Radimation want to set the signal generator to. The “__” of “__freq__” are two “_”.
Set Carrier | Set Carrier is the string that needs to send to set the signal generator carrierlevel. The unit is in dBm, so the string should be made for dBM. |
__carrier__ will be replaced by the value that Radimation want to set the signal generator to. The “__” of “__carrier__ ” are two “_”.
Carrier on | Carrier on is the string that needs to send to set the signal generator carrier on. |
Example: “OUTPUT ON”.
Carrier off | Carrier off is the string that needs to send to set the signal generator carrier off. |
Example: “OUTPUT OFF”.
AM on | AM on is the string that needs to send to set the internal AM generator of the signal generator. The unit of frequency is KHz and the unit of Modulation Depth is %. |
AM off | AM off is the string that needs to send to set the internal am modulation of the signal generator off. |
External on | External on is the string that needs to send to set the modulator to the external input. |
External off | External off is the string that needs to send to set the modulator to the internal input. |
PM on | PM on is the string that needs to send to set the internal PM generator of the signal generator. The unit of frequency is KHz and the unit of duty cycle is %. |
PM off | PM off is the string that needs to send to set the internal PM modulation of the signal generator off. |
Sine Wave | Sine wave is the string that needs to be send when Radimation wants to set the wave form of the internal source to sine. |
Example: “SOURCE2:FUNC SIN”
Square Wave | Square wave is the string that needs to be send when Radimation wants to set the wave form of the internal source to square. |
Example: “SOURCE2:FUNC SQU”
Amplifier
Antenna
Only the start and stop frequency can be set for the amplifier. Chapter generic settings will give more information about the start and stop frequency Coupler
Powermeter
Set frequency | Set Frequency is the string that needs to send to set the powermeter frequency. The unit is in MHz, so the string should be made for MHz. |
__freq__ will be replaced by the value that Radimation want to set the powermeter too. The “__” of “__freq__” are two “_”.
Select Channel | Set Select Channel is the string that Radimation needs to send to set the powermeter channel. This is only necessary when the powermeter has more the one channel. |
Example: “P1,U1”.
Trigger | Trigger is the string that Radimation needs to send to trigger the powermeter. |
Example: “X1”
Result Format | Result Format is the string that Radimation needs to use to decode the value from the string send by the powermeter. The return value is interpreted in dBm. |
Example: “__result__”
__result__ will be replaced by the value that Radimation get from the powermeter. The “__” of “__result__” are two “_”.
Start Zero | Start Zero is the string that Radimation needs to send to start zeroing the powermeter. |
Example: “O1”
Duration | Duration is the time that Radimation waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable result. |
AD converter
Currently unavailable.
Calibration Jigs
Current Sensor
Pre Amplifiers
LISN
Turn Table
Antenna Tower
Absorbing Clamps
Clamp positioner
Cables
Switch matrix
EUT Controller
Messages
Unknown Device Driver
This message box is displayed when Radimation is trying to locate a device driver and was unable to find it. If you see this message please contact your reseller and tell him which driver you are trying to use. The reseller will take action so that you will receive the right device driver.
GPIB: Device is not connected
This message box is displayed when Radimation is unable to connect to a device when using GPIB. Please check the cable and the GPIB device driver address setting.
Device not connected
This message box is displayed when Radimation is unable to connect to the device. Please check cables and device driver settings.
How to make a buscapture
Please verify your settings with the picture showed above and press OK. Now start capturing by pressing the blue arrow pointing to the right. Start Radimation, and perform the test you need to capture. After the test is done, press the button with the red circle. Then select File and then save as to save to hard disk.
Ddlogger.dat
Ddlogger.dat is an output file for a debugging tool used by the software engineers at D.A.R.E!!. The tool is extremely useful for remote problem solving. The general idea is quite simple yet really helpful. Radimation inserts all the communication messages with devices in this file. So the software engineer can see what the software is sending and receiving when it communicates with the devices. With this information the engineer is more capable of reproducing/solving the problem, sometimes in combination with a buscapture. Do you need to install some additional software for this functionality? The answer is no, the tool is integrated in Radimation. But how do I turn it on or off? At startup Radimation looks for the ddlogger.dat file in the root of the drive. When it finds the file it will turn on the debugging tool, otherwise the debugging tool is turned off. What are the consequences for the performance? When the debugging tool is turned on, there is a small performance loss because there is additional writing to the harddisk. Therefore the default should be to run Radimation with the debugging tool turned off.
Step by step procedure
- Make sure Radimation is not running.
- Insert an empty text file in the root of the drive and rename it to “ddlogger.dat”. Make sure that the extension (“.txt”) is also changed.
- Start Radimation, during the start the following screen will appear.
- Select no.
- Perform the measurement you have problems with.
- Close Radimation.
- Send the ddlogger.dat file to D.A.R.E!!, preferably in a compressed file format (Zip)
- Remove the ddlogger.dat file from your harddrive.
AD convertors
National Instruments 6023E 8 Analog inputs
Type of communication: IEEE.
Channels 1:
Hewlett Packard 34401A
Channel 1
Type of measurement: AC Volt
Minimum value: 0Volt
Maximum value: 1 kVolt.
Channel 2:
Minimum value: 0 Amp.
Maximum value: 3 Amp.
Channel 3
Type of measurement: DC Volt
Channel 4:
Maximum value: 3 Amp. (rms)
Channel 5
Minimum value: 0 Ω
Maximum value: 100 MΩ
Channel 6
Minimum value: 0 Hz.
Maximum value: 300 kHz
Channel 7 and 8
Not used
Hewlett Packard 54600
Channel 1:
Type of measurement: V Max.
Maximum value: 1000 Volt.
Channel 2:
Type of measurement: V Min
Minimum value: 0 Volt.
Channel 3
Channel 4:
Channel 5
Minimum value: 0 Hz
Maximum value: 100 kHz
Channel 6
Type of measurement: Period
Minimum value: 0 ms
Maximum value: 10000 ms
Channel 7
Minimum value: 0 ms
Channel 8
Minimum value: 0 ms
Hewlett Packard 3562A
Type of communication: GPIB
Channels
Minimum value: 0 dB
Maximum value: 100 dB
Hewlett Packard 59313
Channel 1
Minimum value: 0
Maximum value: 2048
Channel 2:
Minimum value: 0
Maximum value: 2048
Channel 3
Minimum value: 0
Maximum value: 2048
Channel 4:
Minimum value: 0
Maximum value: 2048
Channel 5 to 8
Not used.
Channels
Marconi 2305
Channel 1
Minimum value: 0
Maximum value: 1000 MHz
Channel 2:
Minimum value: 0
Maximum value: 1000
Channel 3 to 8
Not used.
Fluke 45 AC Current
Channels
Minimum value: 0 mA
Maximum value: 10.000 mA
Fluke 45 DC Current
Channels
Minimum value: 0 mA
Fluke 45 AC Voltage
Channels
Minimum value: 0 mV
Maximum value: 1.000.000 mV
Fluke 45 DC Voltage
Channels
Minimum value: 0 mV
Fluke 45 Frequency
Channels
Minimum value: 0 Hz
Maximum value: 1.000.000 Hz
Fluke 45 Resistance
Channels
Minimum value: 0 Ω
Maximum value: 100.000.000 Ω
LeCroy 9304AM Channel A,B,C,D
Channel 1
Maximum value: 353.55 Volt.
Channel 2:
Channel 3
Channel 4:
Maximum value: 707.1 Volt
Channel 5
Type of measurement: RMS
Maximum value: 250 Volt
Channel 6
Maximum value: 200 MHz
Channel 7 and 8
Not used
Fluke 8840A AC Current
Channels
Minimum value: 0 mA
Fluke 8840A DC Current
Channels
Minimum value: 0 mA
Fluke 8840A AC Voltage
Channels
Minimum value: 0 mV
Fluke 8840A DC Voltage
Channels
Minimum value: 0 mV
Hewlett Packard 3478A AC Current
Channels
Minimum value: 0 mA
Hewlett Packard 3478A DC Current
Channels
Minimum value: 0 mA
Hewlett Packard 3478A AC Voltage
Channels
Minimum value: 0 mV
Maximum value: 300.000 mV
Hewlett Packard 3478A DC Voltage
Channels
Minimum value: 0 mV
Tektronix TDS 400 Series
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Tektronix TDS 500A Series
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Tektronix TDS 600A Series
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Tektronix TDS 3000 Series
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
D.A.R.E!! Development Radimate 2 and 3
Channels 1 to 8
Minimum value: 0
Maximum value: 16383
EPI 575
Channel 1
Minimum value: 0 Hz
Maximum value: 10 kHz
Channel 2:
Channel 3
Minimum value: 0 Hz
Maximum value: 1 MHz.
Channel 4:
Maximum value: 10 MHz.
Channel 5
Minimum value: 0 Hz
Maximum value: 100 MHz
Channel 6
Minimum value: 0 Hz
Maximum value: 1 GHz
Channel 7
Minimum value: 0 Hz
Maximum value: 10 GHz
Channel 8
Minimum value: 0 Hz
Maximum value: 100 GHz
Parallel Port Input 0x3BC and 0x378
Channel 1 to 8