(14 intermediate revisions by 2 users not shown)
Line 8: Line 8:
== Virtual device drivers ==
For testing and demonstration purposes, virtual device drivers can be used and added as well.
Virtual device drivers are devices that act like normal devices but are emulated by software. These virtual device do not physically exist, and thus do not control any real hardware. If a test site with only virtual devices is created, it can be used to perform completely virtual tests.
Virtual device drivers are devices that act like normal devices but are emulated by software. These virtual devices do not physically exist, and thus do not control any real hardware. If a test site with only virtual devices is created, it can be used to perform completely virtual tests.
There are several advantages to include and use virtual device drivers. It is mainly used for debugging, investigating and solving software problems, but is has proven to be very useful when used as a temporarily workaround. For example a test site can have an amplifier which is IEEE controlled and one day somebody accidentally destroys the communication between computer and amplifier. To allow the test engineer to still perform some tests, he can select the virtual amplifier device driver as the amplifier to be used in the test site. The test engineer then only has to set the amplifier in operate manually and will be able to perform the tests that day. When the IEEE communication is repaired the original amplifier device driver can be selected in the testsite again.
==Active device drivers and passive device drivers==
Line 52: Line 52:
Now that all windows have been generally explained, the procedure {{RadiMation}} uses is the following. {{RadiMation}} takes the amount of measurements as defined in the Measure window. After that {{RadiMation}} determines the minimum, maximum and difference. When the difference is equal or smaller then defined in Max difference {{RadiMation}} determines the power. If the difference is greater then defined, {{RadiMation}} takes one new measurement. Replaces the oldest value with the
Now that all windows have been generally explained, the procedure {{RadiMation}} uses is the following. {{RadiMation}} takes the amount of measurements as defined in the Measure window. After that {{RadiMation}} determines the minimum, maximum and difference. When the difference is equal or smaller than defined in Max difference {{RadiMation}} determines the power. If the difference is greater than defined, {{RadiMation}} takes one new measurement. Replaces the oldest value with the
new one. Determines the minimum, maximum and difference again. This continues as long as the difference is larger then defined and the maximum amount of measurement has not yet been reached. If the maximum amount of measurement has been reached the last measurement is taken as the measured value.
Line 61: Line 61:
'''Speed up(2):''' When using a spectrum analyser a small amount of samples may be sufficient to determine the right amount of power. It is up to the engineer to find the right accuracy vs. time setting.
'''Measuring:''' Powermeter who doesn't have a RMS detector, should not be used in Fast constant mode.
'''Measuring:''' Powermeters which do not have a RMS detector, should not be used in Fast constant mode.
Line 77: Line 77:
Now that all windows and buttons have been generally explained, the procedure {{RadiMation}} uses is the following. {{RadiMation}} takes the amount of measurements as defined in the Measure window. After that {{RadiMation}} determines the minimum, maximum and difference. When the difference is equal or smaller then defined in Max difference {{RadiMation}} determines the field. If the difference is greater then defined, {{RadiMation}} takes one new measurement. Replaces the oldest value with the
Now that all windows and buttons have been generally explained, the procedure {{RadiMation}} uses is the following. {{RadiMation}} takes the amount of measurements as defined in the Measure window. After that {{RadiMation}} determines the minimum, maximum and difference. When the difference is equal or smaller than defined in Max difference {{RadiMation}} determines the field. If the difference is greater than defined, {{RadiMation}} takes one new measurement. Replaces the oldest value with the
Line 86: Line 86:
The Axis configuration is a generic driver setting panel.
There are several (old) field sensors which don’t support the read out of an isotropic value: instead they provide the measurements values of all three axes separately.
There are several (old) field sensors which don’t support the readout of an isotropic value: instead they provide the measurement values of all three axes separately.
Using the ‘Software isotropic’ setting in the device driver can then activate that the measurement data of all three axes are being interpret and calculate to the isotropic value and have this isotropic value being return as the measured field strength.
Using the ‘Software isotropic’ setting in the device driver can then activate that the measurement data of all three axes are being interpreted and used to calculate the isotropic value and have this isotropic value being returned as the measured field strength.
When the field sensor already supports the retrieval of the isotropic measurement value, often this value is also returned when the software option is being selected in the device configuration: both isotropic as software isotropic will return the isotropic value of the field sensor. This is depending on the device driver and used equipment.
When the field sensor already supports the retrieval of the isotropic measurement value, often this value is also returned when the software option is being selected in the device configuration: both isotropic as well as software isotropic will return the isotropic value of the field sensor. This is depending on the device driver and used equipment.
Line 138: Line 138:
===RS-232 Setting===
The RS-232 Communication settings are used to specify the RS-232 communication parameters, for the communication with a measurement device over RS-232. A lot of modern measurement devices are connected by USB, however very often then a Virtual RS-232 COMPort (VCP) is generated over the USB connection. In that situation also the RS-232 communication settings should configured.
The RS-232 Communication settings are used to specify the RS-232 communication parameters, for the communication with a measurement device over RS-232. A lot of modern measurement devices are connected by USB, however very often then a Virtual RS-232 COMPort (VCP) is generated over the USB connection. In that situation also the RS-232 communication settings should be configured.
[[Image:RS-232 DeviceStream Configuration.png]]
{{ScreenElementDescription|COM Port|The COM port which {{RadiMation}} has to use to be communicate with the measurement device.}}
{{ScreenElementDescription|COM Port|The COM port which {{RadiMation}} has to be used to communicate with the measurement device.}}
{{ScreenElementDescription|Baudrate|Allows to configure the baudrate that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled.}}
{{ScreenElementDescription|Data bits|Allows to configure the number of data bits that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled.}}
Line 159: Line 159:
{{ScreenElementDescription|Primary Address|The primary address specifies the address of the device, so if the device you want to configure is on address is on 20 you enter 20. Please consult the manual of the device how to determine the GPIB address of the device.}}
{{ScreenElementDescription|Primary Address|The primary address specifies the address of the device, so if the device you want to configure is on address 20 you enter 20. Please consult the manual of the device how to determine the GPIB address of the device.}}
{{ScreenElementDescription|Use advanced configuration|Allows the end-user to enables the more advanced configuration parameters. Those advanced option should only be used if the default settings are not sufficient enough.}}
{{ScreenElementDescription|Use advanced configuration|Allows the end-user to enable the more advanced configuration parameters. Those advanced option should only be used if the default settings are not sufficient.}}
{{ScreenElementDescription|GPIB Board|With GPIB Board you can specify the GPIB board that is used. The default value is 0 and can only be different when multiple GPIB boards are present.}}
{{ScreenElementDescription|Secondary Address|The second address is default 0, and should only be changed when needed. For further information please look in the help of National Instruments 488.2.}}
{{ScreenElementDescription|Secondary Address|The second address is 0 by default, and should only be changed when needed. For further information please look in the help of National Instruments 488.2.}}
{{ScreenElementDescription|GPIB Delay|GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast PC's (> 2.5 GHz). This is most of the time noticeable when a driver is sometimes working and some times gives a GPIB (EABO or TIMO) error. These errors are most of the time, generated randomly. Specifying a GPIB delay time of 3000 uSeconds can fix these random errors. Run the test again and see of the problem as disappeared. Is the problem has disappear then your problem was timing, if not please contact your reseller and report the problems you are having.}}
{{ScreenElementDescription|GPIB Delay|GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast PCs (> 2.5 GHz). This is most of the time noticeable when a driver is sometimes working and sometimes gives a GPIB (EABO or TIMO) error. These errors are most of the time, generated randomly. Specifying a GPIB delay time of 3000 uSeconds can fix these random errors. Run the test again and see if the problem has disappeared. If the problem has disappeared then your problem was timing, if not please contact your reseller and report the problems you are having.}}
{{ScreenElementDescription|Clear device during initialisation|When checked, a low level GPIB command to reset the device will be send to the device during initialisation.}}
{{ScreenElementDescription|Clear device during initialisation|When checked, a low level GPIB command to reset the device will be sent to the device during initialisation.}}
{{ScreenElementDescription|Readdress device|When checked, a low level GPIB command to select the correct address will be transmitted every time a command is send to the device.}}
{{ScreenElementDescription|Readdress device|When checked, a low level GPIB command to select the correct address will be transmitted every time a command is sent to the device.}}
=== VISA Settings ===
The VISA Communication settings are used to specify the VISA communication parameters, for the communication with a measurement device. The VISA library is a higher level communication library that supports different kind of communication methods. {{RadiMation}} doesn't provide a VISA library itself, and thus requires that a VISA library from another supplier like [[National Instruments]] or [[Keysight Technologies]] is installed. The VISA manager that is provided by that VISA library can be used to determine the correct VISA resource. The selected VISA configuration thus also has influence if a measurement device is controlled by GPIB, RS-232, LAN, USB-TMC, VXI11, network-socket or another communication method .
The VISA Communication settings are used to specify the VISA communication parameters, for the communication with a measurement device. The VISA library is a higher level communication library that supports different kinds of communication methods. {{RadiMation}} doesn't provide a VISA library itself, and thus requires that a VISA library from another supplier like [[National Instruments]] or [[Keysight Technologies]] is installed. The VISA manager that is provided by that VISA library can be used to determine the correct VISA resource. The selected VISA configuration thus also has an influence if a measurement device is controlled by GPIB, RS-232, LAN, USB-TMC, VXI11, network-socket or another communication method .
[[Image:VISA DeviceStream Configuration.png]]
Line 180: Line 180:
{{ScreenElementDescription|Visa-ID|Allows to specify a VISA Identifier that should be used for the communication with the measurement device. Any VISA Identifier that is supported by VISA is accepted. If one of the other communication methods is selected the corresponding VISA Identifier is also shown in this setting. Often used VISA identifiers are:
* <code>TCPIP[board]::<IP-address>::INSTR</code>: VXI11 or LXI ethernet communication with the device with '<IP-address>'.
* <code>TCPIP[board]::<IP-address>::<port-number>::SOCKET</code>: Raw socket based ethernet communication with on the port '<port-number>' with the the device '<IP-address>'
* <code>TCPIP[board]::<IP-address>::<port-number>::SOCKET</code>: Raw socket based ethernet communication on the port '<port-number>' with the the device '<IP-address>'
* <code>GPIB[board]::<primary address>::INSTR</code>: GPIB communication to the GPIB device with the address '<primary address>'
* <code>ASRL<port>::INSTR</code>: Serial communcation on COM-port '<port>'
Line 187: Line 187:
=== USB Settings ===
The USB Communication settings are used to specify that an USB connection to a DARE!! Instruments measurement device is used. It is not possible to use this USB communication setting for devices that simulate a Virtual COMPort (VCP) over an USB connection. The RS232 Settings should be used for such a kind of measurement device.
The USB Communication settings are used to specify that a USB connection to a DARE!! Instruments measurement device is used. It is not possible to use this USB communication setting for devices that simulate a Virtual COMPort (VCP) over a USB connection. The RS232 Settings should be used for such a kind of measurement device.
{{ScreenElementDescription|Device Identifier|The device identifier (which is an unique identifier of 8 groups of digits) that identifies the measurement device that is connected over USB.}}
{{ScreenElementDescription|Device Identifier|The device identifier (which is a unique identifier of 8 groups of digits) that identifies the measurement device that is connected over USB.}}
{{ScreenElementDescription|Detect|Will automatically determine the correct {{ScreenElement|Device Identifier}} for the measurement device that is connected.}}
Line 206: Line 206:
==Configurable device drivers==
{{RadiMation}} allows the user to create its own device drivers for test and measurement equipment, which is (not yet) implemented in the standard device driver list.
{{RadiMation}} allows the user to create their own device drivers for test and measurement equipment, which is (not yet) implemented in the standard device driver list.
Line 215: Line 215:
# Select the driver called “Configurable xx” (i.e. if you want to make a signal generator device driver you would select the “Configurable signal generator” device driver).
# Enter a description for the device driver (for example the type number of the generator) and press OK.
# The name of the device driver will be added in the available device driver’s list.
# The name of the device driver will be added in the available device drivers list.
# Select the new device driver from the available device device’s list.
# Select the new device driver from the available device drivers list.
# Press the “Edit” button.
# A configuration screen for the device driver will appear. All required control commands for the device must be entered. Refer to the operating manual of the equipment for these codes.
# A configuration screen for the device driver will appear. For active controlled equipment all required control commands for the device must be entered. Refer to the operating manual of the equipment for these codes.
Line 224: Line 224:
===Generic settings===
{{ScreenElementDescription|Start and stop frequency|The default value for the start frequency is 1 Hz and for the stop frequency is 120 GHz. The creator of the device is encouraged to set the correct start and stop frequency. If the start and stop frequency are set correctly, {{RadiMation}} can warn the test engineer when he/she want to use the device out of its valid frequency range.}}
{{ScreenElementDescription|Start and stop frequency|The default value for the start frequency is 1 Hz and for the stop frequency is 120 GHz. The creator of the device is encouraged to set the correct start and stop frequency. If the start and stop frequency are set correctly, {{RadiMation}} can warn the test engineer when they want to use the device out of its valid frequency range.}}
{{ScreenElementDescription|Reset|In the reset window you need to specify the string that the software needs to send when it want to reset the device. For example *RST is commonly used reset string. If you don’t know the string then leave this window blank, and make sure that the device in a neutral state.}}
{{ScreenElementDescription|Init|In the init window you need to specify the string that the software needs to send when it want to Init  the device. For example *RST is commonly used reset string.}}
{{ScreenElementDescription|Get ID|In the Get ID window you need to specify the string that the software needs to send when it want to get the ID string of the device. For example *IDN? is commonly used Get ID string.}}
{{ScreenElementDescription|Get ID|In the Get ID window you need to specify the string that the software needs to send when it wants to get the ID string of the device. For example *IDN? is commonly used Get ID string.}}
{{ScreenElementDescription|Returned ID|In the Returned ID window you need to specify the string that the software will receive so that it know that it has the right device. For example "Hewlett_Packard,8643A," can be used for the Hewlett Packard 8643A. If you leave this window empty then all returned strings are accepted.}}
{{ScreenElementDescription|Returned ID|In the Returned ID window you need to specify the string that the software will receive so that it knows that it has the right device. For example "Hewlett_Packard,8643A," can be used for the Hewlett Packard 8643A. If you leave this window empty then all returned strings are accepted.}}
Line 234: Line 234:
[[Image:Configurable Signal Generator Window.png]]
{{ScreenElementDescription|Set Frequency|Set Frequency is the string that needs to send to set the signal generator frequency. The unit is in MHZ, so the string should be made for MHz. }}
{{ScreenElementDescription|Set Frequency|Set Frequency is the string that needs to be sent to set the signal generator frequency. The unit is in MHZ, so the string should be made for MHz. }}
'''Example:''' “FRQ__freq__MHZ”.
Line 248: Line 248:
__freq__ will be replaced by the value that {{RadiMation}} want to set the signal generator to.  The “__” of  “__freq__” are two “_”.
{{ScreenElementDescription|Set Carrier|Set Carrier is the string that needs to send to set the signal generator carrierlevel. The unit is in dBm, so the string should be made for dBM.}}
{{ScreenElementDescription|Set Carrier|Set Carrier is the string that needs to be sent to set the signal generator carrierlevel. The unit is in dBm, so the string should be made for dBM.}}
'''Example:''' “:SOURCE:POWER __carrier__ DBM”.
__carrier__ will be replaced by the value that {{RadiMation}} want to set the signal generator to.  The “__” of  “__carrier__ ” are two “_”.
__carrier__ will be replaced by the value that {{RadiMation}} wants to set the signal generator to.  The “__” of  “__carrier__ ” are two “_”.
{{ScreenElementDescription|Carrier on|Carrier on is the string that needs to send to set the signal generator carrier on.}}
{{ScreenElementDescription|Carrier on|Carrier on is the string that needs to be sent to set the signal generator carrier on.}}
'''Example:''' “OUTPUT ON”.
{{ScreenElementDescription|Carrier off|Carrier off is the string that needs to send to set the signal generator carrier off.}}
{{ScreenElementDescription|Carrier off|Carrier off is the string that needs to be sent to set the signal generator carrier off.}}
'''Example:''' “OUTPUT OFF”.
{{ScreenElementDescription|AM on|AM on is the string that needs to send to set the internal AM generator of the signal generator. The unit of frequency is KHz and the unit of Modulation Depth is %.}}
{{ScreenElementDescription|AM on|AM on is the string that needs to be sent to set the internal AM generator of the signal generator. The unit of frequency is KHz and the unit of Modulation Depth is %.}}
'''Example:''' “SOURCE2:FREQ  __freq__  KHZ;SOURCE:AM:DEPTH  __depth__ PCT;SOURCE:AM:STATE ON”.
Line 269: Line 269:
“__freq__  ” are two “_”.
{{ScreenElementDescription|AM off|AM off is the string that needs to send to set the internal am modulation of the signal generator off.}}
{{ScreenElementDescription|AM off|AM off is the string that needs to be sent to set the internal am modulation of the signal generator off.}}
'''Example:''' “SOURCE:AM:STATE OFF”.
{{ScreenElementDescription|External on|External on is the string that needs to send to set the modulator to the external input.}}
{{ScreenElementDescription|External on|External on is the string that needs to be sent to set the modulator to the external input.}}
'''Example:''' “SOURCE:AM:SOURCE EXT”.
{{ScreenElementDescription|External off|External off is the string that needs to send to set the modulator to the internal input.}}
{{ScreenElementDescription|External off|External off is the string that needs to be sent to set the modulator to the internal input.}}
'''Example:''' “SOURCE:AM:SOURCE INT”.
{{ScreenElementDescription|PM on|PM on is the string that needs to send to set the internal PM generator of the signal generator. The unit of frequency is KHz and the unit of duty cycle is %.}}
{{ScreenElementDescription|PM on|PM on is the string that needs to be sent to set the internal PM generator of the signal generator. The unit of frequency is KHz and the unit of duty cycle is %.}}
'''Example:''' “SOURCE2:FREQ  __freq__  KHZ;SOURCE:PM:DUTY  __duty__ PCT;SOURCE:PM:STATE ON”.
Line 288: Line 288:
{{ScreenElementDescription|PM off|PM off is the string that needs to send to set the internal PM modulation of the signal generator off.}}
{{ScreenElementDescription|PM off|PM off is the string that needs to be sent to set the internal PM modulation of the signal generator off.}}
'''Example:''' “SOURCE:PM:STATE OFF”.
{{ScreenElementDescription|Sine Wave|Sine wave is the string that needs to be send when {{RadiMation}} wants to set the wave form of the internal source to sine.}}
{{ScreenElementDescription|Sine Wave|Sine wave is the string that needs to be sent when {{RadiMation}} wants to set the wave form of the internal source to sine.}}
'''Example:''' “SOURCE2:FUNC SIN”
{{ScreenElementDescription|Square Wave|Square wave is the string that needs to be send when {{RadiMation}} wants to set the wave form of the internal source to square.}}
{{ScreenElementDescription|Square Wave|Square wave is the string that needs to be sent when {{RadiMation}} wants to set the wave form of the internal source to square.}}
'''Example:''' “SOURCE2:FUNC SQU”
Line 310: Line 310:
[[Image:Configurable Power Meter Window.png]]
{{ScreenElementDescription|Set frequency|Set Frequency is the string that needs to send to set the powermeter frequency. The unit is in MHz, so the string should be made for MHz.}}
{{ScreenElementDescription|Set frequency|Set Frequency is the string that needs to be sent to set the powermeter frequency. The unit is in MHz, so the string should be made for MHz.}}
Line 324: Line 324:
'''Example:''' “X1”
'''Example:''' “X1”
{{ScreenElementDescription|Result Format|Result Format is the string that {{RadiMation}} needs to use to decode the value from the string send by the powermeter. The return value is interpreted in dBm.}}
{{ScreenElementDescription|Result Format|Result Format is the string that {{RadiMation}} needs to use to decode the value from the string sent by the powermeter. The return value is interpreted in dBm.}}
'''Example:''' “__result__”
Line 335: Line 335:
'''Example:''' “O1”
'''Example:''' “O1”
{{ScreenElementDescription|Duration|Duration is the time that {{RadiMation}} waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable result.}}
{{ScreenElementDescription|Duration|Duration is the time that {{RadiMation}} waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable results.}}
=== Configurable AD converter ===
Line 381: Line 381:
[[Image:Amplifier Device Driver Can Not Be Configured Window.png]]
===Unknown Device Driver===
Line 401: Line 401:
==How to Report an Error==
When encountering a problem with the software you might would like to report it to the RadiMation support.
When encountering a problem with the software you might like to report it to the RadiMation support.
The RadiMation error popups, contains detailed section. This can be expanded with details button on the error popup.
The RadiMation error popups, contains a detailed section. This can be expanded with the details button on the error popup.
In the expanded detailed error popup, a Report Error button is present. This allows Error Reporting to the RadiMation support within RadiMation.
More information about Error Reporting can be found here:
Latest revision as of 12:19, 18 February 2025
Device drivers[edit]
Virtual device drivers[edit]
  • Usable frequency range
  • Maximum input power
Signal generator[edit]
Amplifier[edit]
Antenna[edit]
Coupler[edit]
Powermeter[edit]
Measuring: Powermeters which do not have a RMS detector, should not be used in Fast constant mode.
Field Sensor[edit]
Axis setting panel[edit]
AD converter[edit]
Injection device[edit]
Calibration Jigs[edit]
Current Sensor[edit]
Pre Amplifiers[edit]
LISN[edit]
Turn Table[edit]
Antenna Tower[edit]
Absorbing Clamps[edit]
Clamp positioner[edit]
Cables[edit]
Switch matrix[edit]
EUT Controller[edit]
Communication settings[edit]
RS-232 Setting[edit]
ScreenElementDescription.svg COM Port The COM port which RadiMation® has to be used to communicate with the measurement device.
ScreenElementDescription.svg Baudrate Allows to configure the baudrate that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled.
GPIB Setting[edit]
ScreenElementDescription.svg Primary Address The primary address specifies the address of the device, so if the device you want to configure is on address 20 you enter 20. Please consult the manual of the device how to determine the GPIB address of the device.
ScreenElementDescription.svg Use advanced configuration Allows the end-user to enable the more advanced configuration parameters. Those advanced option should only be used if the default settings are not sufficient.
ScreenElementDescription.svg Secondary Address The second address is 0 by default, and should only be changed when needed. For further information please look in the help of National Instruments 488.2.
ScreenElementDescription.svg GPIB Delay GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast PCs (> 2.5 GHz). This is most of the time noticeable when a driver is sometimes working and sometimes gives a GPIB (EABO or TIMO) error. These errors are most of the time, generated randomly. Specifying a GPIB delay time of 3000 uSeconds can fix these random errors. Run the test again and see if the problem has disappeared. If the problem has disappeared then your problem was timing, if not please contact your reseller and report the problems you are having.
ScreenElementDescription.svg Clear device during initialisation When checked, a low level GPIB command to reset the device will be sent to the device during initialisation.
ScreenElementDescription.svg Readdress device When checked, a low level GPIB command to select the correct address will be transmitted every time a command is sent to the device.
VISA Settings[edit]
The VISA Communication settings are used to specify the VISA communication parameters, for the communication with a measurement device. The VISA library is a higher level communication library that supports different kinds of communication methods. RadiMation® doesn't provide a VISA library itself, and thus requires that a VISA library from another supplier like National Instruments or Keysight Technologies is installed. The VISA manager that is provided by that VISA library can be used to determine the correct VISA resource. The selected VISA configuration thus also has an influence if a measurement device is controlled by GPIB, RS-232, LAN, USB-TMC, VXI11, network-socket or another communication method .
ScreenElementDescription.svg Alias Allows to specify a VISA Alias that should be used for the communication with the measurement device. Any Alias that is supported by VISA is accepted. The correct Alias can be determined by using the VISA manager (eg. National Instruments MAX) that is installed on the PC.
ScreenElementDescription.svg LAN Allows to specify that a VXI11 or LXI connection should be used for the communication with the measurement device. It is possible to specify the IP-address or the (FQDN) hostname of the measurement device.
  • TCPIP[board]::<IP-address>::INSTR: VXI11 or LXI ethernet communication with the device with '<IP-address>'.
  • TCPIP[board]::<IP-address>::<port-number>::SOCKET: Raw socket based ethernet communication on the port '<port-number>' with the the device '<IP-address>'
USB Settings[edit]
ScreenElementDescription.svg Device Identifier The device identifier (which is a unique identifier of 8 groups of digits) that identifies the measurement device that is connected over USB.
TCPIP Settings[edit]
The TCPIP Communication settings are used to specify that a socket based TCPIP connection to a measurement device should be used.
  2. Press the “New” button.
  5. The name of the device driver will be added in the available device drivers list.
  6. Select the new device driver from the available device drivers list.
  7. Press the “Edit” button.
Generic settings[edit]
ScreenElementDescription.svg Start and stop frequency The default value for the start frequency is 1 Hz and for the stop frequency is 120 GHz. The creator of the device is encouraged to set the correct start and stop frequency. If the start and stop frequency are set correctly, RadiMation® can warn the test engineer when they want to use the device out of its valid frequency range.
ScreenElementDescription.svg Get ID In the Get ID window you need to specify the string that the software needs to send when it wants to get the ID string of the device. For example *IDN? is commonly used Get ID string.
ScreenElementDescription.svg Returned ID In the Returned ID window you need to specify the string that the software will receive so that it knows that it has the right device. For example "Hewlett_Packard,8643A," can be used for the Hewlett Packard 8643A. If you leave this window empty then all returned strings are accepted.
ScreenElementDescription.svg Set Frequency Set Frequency is the string that needs to be sent to set the signal generator frequency. The unit is in MHZ, so the string should be made for MHz.
Example: “FRQ__freq__MHZ”.
Example: “FRQ__freqHz__HZ”.
Example: “FRQ__freqkHz__KHZ”.
Example: “FRQ__freqMHz__MHZ”.
Example: “FRQ__freqGHz__GHZ”.
ScreenElementDescription.svg Set Carrier Set Carrier is the string that needs to be sent to set the signal generator carrierlevel. The unit is in dBm, so the string should be made for dBM.
ScreenElementDescription.svg Carrier on Carrier on is the string that needs to be sent to set the signal generator carrier on.
Example: “OUTPUT ON”.
ScreenElementDescription.svg Carrier off Carrier off is the string that needs to be sent to set the signal generator carrier off.
Example: “OUTPUT OFF”.
ScreenElementDescription.svg AM on AM on is the string that needs to be sent to set the internal AM generator of the signal generator. The unit of frequency is KHz and the unit of Modulation Depth is %.
ScreenElementDescription.svg AM off AM off is the string that needs to be sent to set the internal am modulation of the signal generator off.
ScreenElementDescription.svg External on External on is the string that needs to be sent to set the modulator to the external input.
ScreenElementDescription.svg External off External off is the string that needs to be sent to set the modulator to the internal input.
ScreenElementDescription.svg PM on PM on is the string that needs to be sent to set the internal PM generator of the signal generator. The unit of frequency is KHz and the unit of duty cycle is %.
ScreenElementDescription.svg PM off PM off is the string that needs to be sent to set the internal PM modulation of the signal generator off.
ScreenElementDescription.svg Sine Wave Sine wave is the string that needs to be sent when RadiMation® wants to set the wave form of the internal source to sine.
Example: “SOURCE2:FUNC SIN”
ScreenElementDescription.svg Square Wave Square wave is the string that needs to be sent when RadiMation® wants to set the wave form of the internal source to square.
Example: “SOURCE2:FUNC SQU”
Configurable Amplifier[edit]
Main[edit]
Operation[edit]
Example[edit]
1 = RF ON
1 = BAND 2
1 = LINE ON
Configurable Antenna[edit]
Configurable Powermeter[edit]
ScreenElementDescription.svg Set frequency Set Frequency is the string that needs to be sent to set the powermeter frequency. The unit is in MHz, so the string should be made for MHz.
Example: “P1,U1”.
Example: “X1”
ScreenElementDescription.svg Result Format Result Format is the string that RadiMation® needs to use to decode the value from the string sent by the powermeter. The return value is interpreted in dBm.
Example: “__result__”
Example: “O1”
ScreenElementDescription.svg Duration Duration is the time that RadiMation® waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable results.
Channels[edit]
Read Back examples[edit]
Communication[edit]
Configurable LISN[edit]
Configurable Turn Table[edit]
Configurable commands[edit]
Check device[edit]
Device is initialised[edit]
Device is deinitialised[edit]
Some examples are:
Communication[edit]
Identification[edit]
Antenna Tower[edit]
Antenna Tower Advanced[edit]
Currently unavailable.
Configurable Cable[edit]
sending the next command.
keyword inserted value
__calculatedvoltage__ The calculated voltage expressed in V.
Messages[edit]
Unknown Device Driver[edit]
Device not connected[edit]
How to Report an Error[edit]
AD convertors[edit]
Type of communication: IEEE.
Channels 1:
Hewlett Packard 34401A[edit]
Channel 1
Type of measurement: AC Volt
Minimum value: 0Volt
Maximum value: 1 kVolt.
Channel 2:
Minimum value: 0 Amp.
Maximum value: 3 Amp.
Channel 3
Type of measurement: DC Volt
Channel 4:
Maximum value: 3 Amp. (rms)
Channel 5
Minimum value: 0 Ω
Maximum value: 100 MΩ
Channel 6
Minimum value: 0 Hz.
Maximum value: 300 kHz
Channel 7 and 8
Not used
Hewlett Packard 54600[edit]
Channel 1:
Type of measurement: V Max.
Maximum value: 1000 Volt.
Channel 2:
Type of measurement: V Min
Minimum value: 0 Volt.
Channel 3
Channel 4:
Channel 5
Minimum value: 0 Hz
Maximum value: 100 kHz
Channel 6
Type of measurement: Period
Minimum value: 0 ms
Maximum value: 10000 ms
Channel 7
Minimum value: 0 ms
Channel 8
Minimum value: 0 ms
Hewlett Packard 3562A[edit]
Type of communication: GPIB
Channels
Minimum value: 0 dB
Maximum value: 100 dB
Hewlett Packard 59313[edit]
Channel 1
Minimum value: 0
Maximum value: 2048
Channel 2:
Minimum value: 0
Maximum value: 2048
Channel 3
Minimum value: 0
Maximum value: 2048
Channel 4:
Minimum value: 0
Maximum value: 2048
Channel 5 to 8
Not used.
Channels
Marconi 2305[edit]
Channel 1
Minimum value: 0
Maximum value: 1000 MHz
Channel 2:
Minimum value: 0
Maximum value: 1000
Channel 3 to 8
Not used.
Fluke 45 AC Current[edit]
Channels
Minimum value: 0 mA
Maximum value: 10.000 mA
Fluke 45 DC Current[edit]
Channels
Minimum value: 0 mA
Fluke 45 AC Voltage[edit]
Channels
Minimum value: 0 mV
Maximum value: 1.000.000 mV
Fluke 45 DC Voltage[edit]
Channels
Minimum value: 0 mV
Fluke 45 Frequency[edit]
Channels
Minimum value: 0 Hz
Maximum value: 1.000.000 Hz
Fluke 45 Resistance[edit]
Channels
Minimum value: 0 Ω
Maximum value: 100.000.000 Ω
Channel 1
Maximum value: 353.55 Volt.
Channel 2:
Channel 3
Channel 4:
Maximum value: 707.1 Volt
Channel 5
Type of measurement: RMS
Maximum value: 250 Volt
Channel 6
Maximum value: 200 MHz
Channel 7 and 8
Not used
Fluke 8840A AC Current[edit]
Channels
Minimum value: 0 mA
Fluke 8840A DC Current[edit]
Channels
Minimum value: 0 mA
Fluke 8840A AC Voltage[edit]
Channels
Minimum value: 0 mV
Fluke 8840A DC Voltage[edit]
Channels
Minimum value: 0 mV
Channels
Minimum value: 0 mA
Channels
Minimum value: 0 mA
Channels
Minimum value: 0 mV
Maximum value: 300.000 mV
Channels
Minimum value: 0 mV
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Channels 1 to 8
Minimum value: 0
Maximum value: 16383
EIP 575[edit]
Channel 1
Minimum value: 0 Hz
Maximum value: 10 kHz
Channel 2:
Channel 3
Minimum value: 0 Hz
Maximum value: 1 MHz.
Channel 4:
Maximum value: 10 MHz.
Channel 5
Minimum value: 0 Hz
Maximum value: 100 MHz
Channel 6
Minimum value: 0 Hz
Maximum value: 1 GHz
Channel 7
Minimum value: 0 Hz
Maximum value: 10 GHz
Channel 8
Minimum value: 0 Hz
Maximum value: 100 GHz
Channel 1 to 8