Difference between revisions of "Chapter 15"
(→Calibration Jigs) |
(→Configurable device drivers) |
(17 intermediate revisions by 3 users not shown) | |||
= Device drivers = | = Device drivers = | ||
− | Device drivers are | + | Device drivers are available in {{Radimation}} to make it possible to communicate with thousands of different test and measurement equipment devices. They make the system flexible to use different devices, while the {{RadiMation}} Core stays generic. The {{RadiMation}} Core does not even know how to control specific devices it is controlling, only the type of device, and which device driver to use. The device driver is responsible for the communication between the {{RadiMation}} core and the specific test and measurement equipment, by sending the correct commands to the devices. If for example a new spectrum analyser or signal generator has been acquired, it is only needed to configure the corresponding device driver in the {{RadiMation}} software, and it will be able to use the new device. All the configurations of all the tests will remain the same. |
This chapter only describes the device driver specific configuration. All the configuration of the device drivers that are managed by the {{RadiMation}} Core, are described in {{ManualLink|14|3. Device Driver configuration}}. Also the common device driver settings are described in {{ManualLink|14|Device Driver Settings}}. | This chapter only describes the device driver specific configuration. All the configuration of the device drivers that are managed by the {{RadiMation}} Core, are described in {{ManualLink|14|3. Device Driver configuration}}. Also the common device driver settings are described in {{ManualLink|14|Device Driver Settings}}. | ||
− | ==Virtual device drivers== | + | == Virtual device drivers == |
− | For testing and demonstration purposes, virtual device drivers | + | For testing and demonstration purposes, virtual device drivers can be used and added as well. |
+ | Virtual device drivers are devices that act like normal devices but are emulated by software. These virtual device do not physically exist, and thus do not control any real hardware. If a test site with only virtual devices is created, it can be used to perform completely virtual tests. | ||
Virtual device drivers do not have limitations like normal device drivers (like frequency band, maximum power, sweep times, etc.) | Virtual device drivers do not have limitations like normal device drivers (like frequency band, maximum power, sweep times, etc.) | ||
− | == | + | There are several advantages to include and use virtual device drivers. It is mainly used for debugging, investigating and solving software problems, but is has proven to be very useful when used as a temporarily workaround. For example a test site can have an amplifier which is IEEE controlled and one day somebody accidentally destroys the communication between computer and amplifier. To allow the test engineer to still perform some tests, he can select the virtual amplifier device driver as the amplifier to be used in the test site. The test engineer then only has to set the amplifier in operate manually and will be able to perform the tests that day. When the IEEE communication is repaired the original amplifier device driver can be selected in the testsite again. |
− | {{RadiMation}} supports two types of device drivers | + | |
+ | ==Active device drivers and passive device drivers== | ||
+ | {{RadiMation}} supports two types of device drivers: active and passive device drivers. | ||
+ | Active devices are test and measurement equipment like [[powermeter]], [[signal generator]]s, [[spectrum analyser]]s, [[field sensor]]s, etc. For these devices the communication settings (like the IEEE address or the serial port) can be set which {{RadiMation}} has to use to be able to communicate with these devices. | ||
+ | Passive devices are test and measurement equipment like [[coupler]]s, [[antenna]], [[cable]]s, [[calibration jig]]s, [[current sensor]]s, etc. Passive equipment do also need a device driver. | ||
+ | The reason for this is that {{RadiMation}} also has to know a number of details for these devices. Among others, the following information is relevant: | ||
+ | * Usable frequency range | ||
+ | * Maximum input power | ||
+ | * General information of the device, to include a list of used equipment during a test in the report | ||
+ | * Correction files that are relevant for the device | ||
+ | With this information {{RadiMation}} can prevent the test engineer from making large mistakes, like for example using a [[coupler]] in an unsupported frequency range. | ||
==Device specific configuration== | ==Device specific configuration== | ||
Line 122: | Line 135: | ||
== Communication settings == | == Communication settings == | ||
− | Depending on the brand and model of the device, it may be necessary to specify the parameters for the communication with the device. The GPIB/IEEE 488 and | + | Depending on the brand and model of the device, it may be necessary to specify the parameters for the communication with the device. The GPIB/IEEE-488 and RS-232 buses are most commonly used. This section describes which communication buses are supported and which communication parameters can be configured. Not all devices support all the communication buses, so only the applicable communication buses can be selected in the device driver configuration. |
===RS-232 Setting=== | ===RS-232 Setting=== | ||
Line 146: | Line 159: | ||
− | {{ScreenElementDescription|Primary Address|The primary address specifies the address of the device, so if the device you want to configure is on address is on 20 you enter 20. Please consult the manual of the device how to determine the GPIB address of the device. }} | + | {{ScreenElementDescription|Primary Address|The primary address specifies the address of the device, so if the device you want to configure is on address is on 20 you enter 20. Please consult the manual of the device how to determine the GPIB address of the device.}} |
{{ScreenElementDescription|Use advanced configuration|Allows the end-user to enables the more advanced configuration parameters. Those advanced option should only be used if the default settings are not sufficient enough.}} | {{ScreenElementDescription|Use advanced configuration|Allows the end-user to enables the more advanced configuration parameters. Those advanced option should only be used if the default settings are not sufficient enough.}} | ||
{{ScreenElementDescription|GPIB Board|With GPIB Board you can specify the GPIB board that is used. The default value is 0 and can only be different when multiple GPIB boards are present.}} | {{ScreenElementDescription|GPIB Board|With GPIB Board you can specify the GPIB board that is used. The default value is 0 and can only be different when multiple GPIB boards are present.}} | ||
{{ScreenElementDescription|Secondary Address|The second address is default 0, and should only be changed when needed. For further information please look in the help of National Instruments 488.2.}} | {{ScreenElementDescription|Secondary Address|The second address is default 0, and should only be changed when needed. For further information please look in the help of National Instruments 488.2.}} | ||
{{ScreenElementDescription|GPIB Delay|GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast PC's (> 2.5 GHz). This is most of the time noticeable when a driver is sometimes working and some times gives a GPIB (EABO or TIMO) error. These errors are most of the time, generated randomly. Specifying a GPIB delay time of 3000 uSeconds can fix these random errors. Run the test again and see of the problem as disappeared. Is the problem has disappear then your problem was timing, if not please contact your reseller and report the problems you are having.}} | {{ScreenElementDescription|GPIB Delay|GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast PC's (> 2.5 GHz). This is most of the time noticeable when a driver is sometimes working and some times gives a GPIB (EABO or TIMO) error. These errors are most of the time, generated randomly. Specifying a GPIB delay time of 3000 uSeconds can fix these random errors. Run the test again and see of the problem as disappeared. Is the problem has disappear then your problem was timing, if not please contact your reseller and report the problems you are having.}} | ||
− | {{ScreenElementDescription|Clear device during initialisation| | + | {{ScreenElementDescription|Clear device during initialisation|When checked, a low level GPIB command to reset the device will be send to the device during initialisation.}} |
− | {{ScreenElementDescription|Readdress device| | + | {{ScreenElementDescription|Readdress device|When checked, a low level GPIB command to select the correct address will be transmitted every time a command is send to the device.}} |
Line 192: | Line 205: | ||
− | == | + | ==Configurable device drivers== |
− | + | {{RadiMation}} allows the user to create its own device drivers for test and measurement equipment, which is (not yet) implemented in the standard device driver list. | |
− | + | User configurable device drivers are available for nearly all types of test and measurement equipment. However, device drivers for spectrum analysers and (scanning) receivers can not be made with user configurable device drivers because the complexity (and differences between suppliers) of these devices is too high. | |
− | User configurable device drivers are available for nearly all types of test equipment. However, device drivers for spectrum analysers and | ||
To make your own device driver, use the “Device drivers” tab in the “Configuration” > “Configuration” menu and follow the steps below: | To make your own device driver, use the “Device drivers” tab in the “Configuration” > “Configuration” menu and follow the steps below: | ||
+ | # In the device driver’s menu, select the required device driver type. | ||
+ | # Press the “New” button. | ||
+ | # Select the driver called “Configurable xx” (i.e. if you want to make a signal generator device driver you would select the “Configurable signal generator” device driver). | ||
+ | # Enter a description for the device driver (for example the type number of the generator) and press OK. | ||
+ | # The name of the device driver will be added in the available device driver’s list. | ||
+ | # Select the new device driver from the available device device’s list. | ||
+ | # Press the “Edit” button. | ||
+ | # A configuration screen for the device driver will appear. For active controlled equipment all required control commands for the device must be entered. Refer to the operating manual of the equipment for these codes. | ||
− | + | After all codes are entered, the device driver is ready for use. The custom-made device driver can then be used as any other device driver by selecting the driver in the Equipment list. | |
− | After all codes are entered, the device driver is ready for use. | ||
− | The custom-made device driver can be used as any other device driver by selecting the driver in the Equipment list. | ||
===Generic settings=== | ===Generic settings=== | ||
Line 232: | Line 231: | ||
− | ===Signal generator=== | + | === Configurable Signal generator === |
[[Image:Configurable Signal Generator Window.png]] | [[Image:Configurable Signal Generator Window.png]] | ||
Line 301: | Line 300: | ||
'''Example:''' “SOURCE2:FUNC SQU” | '''Example:''' “SOURCE2:FUNC SQU” | ||
− | ===Amplifier=== | + | === Configurable Amplifier === |
+ | {{:Configurable Amplifier}} | ||
− | + | === Configurable Antenna === | |
+ | {{:Configurable Antenna}} | ||
− | === | + | === Configurable Powermeter === |
[[Image:Configurable Power Meter Window.png]] | [[Image:Configurable Power Meter Window.png]] | ||
Line 340: | Line 337: | ||
{{ScreenElementDescription|Duration|Duration is the time that {{RadiMation}} waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable result.}} | {{ScreenElementDescription|Duration|Duration is the time that {{RadiMation}} waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable result.}} | ||
− | === | + | === Configurable AD converter === |
{{:Configurable_AD_Convertor}} | {{:Configurable_AD_Convertor}} | ||
Line 348: | Line 343: | ||
{{:Configurable Calibration Jig}} | {{:Configurable Calibration Jig}} | ||
− | ===Current Sensor=== | + | === Configurable Current Sensor === |
Only the start and stop frequency can be set for the amplifier. Chapter generic settings will give more information about the start and stop frequency | Only the start and stop frequency can be set for the amplifier. Chapter generic settings will give more information about the start and stop frequency | ||
− | ===Pre | + | === Configurable Pre Amplifier === |
− | ===Receivers / Spectrum analyser=== | + | === Configurable Receivers / Spectrum analyser === |
− | + | Due to the complexity of controlling analysers and (scanning) receivers, no configurable device driver is available for analyser and (scanning) receivers. | |
− | ===LISN=== | + | === Configurable LISN === |
+ | {{:Configurable LISN}} | ||
− | + | === Configurable Turn Table=== | |
− | ===Turn Table=== | ||
{{:Configurable TurnTable}} | {{:Configurable TurnTable}} | ||
− | ===Antenna Tower=== | + | === Configurable Antenna Tower=== |
− | + | {{:Configurable Antenna Tower}} | |
+ | === Configurable Absorbing Clamps=== | ||
− | ===Clamp positioner=== | + | === Configurable Clamp positioner=== |
Currently unavailable. | Currently unavailable. | ||
− | === | + | === Configurable Cable=== |
− | ===Switch matrix=== | + | === Configurable Switch matrix=== |
− | + | {{:Configurable Switch Matrix}} | |
− | + | {{:Configurable EUT Controller}} | |
==Messages == | ==Messages == | ||
Line 420: | Line 405: | ||
In the expanded detailed error popup, a Report Error button is present. This allows Error Reporting to the RadiMation support within RadiMation. | In the expanded detailed error popup, a Report Error button is present. This allows Error Reporting to the RadiMation support within RadiMation. | ||
More information about Error Reporting can be found here: | More information about Error Reporting can be found here: | ||
− | + | https://wiki.radimation.com/wiki/index.php/Error_Report | |
[[File:ErrorPopupWindow.png]] | [[File:ErrorPopupWindow.png]] |
Latest revision as of 07:47, 8 May 2023
Device drivers
Introduction
For testing and demonstration purposes, virtual device drivers can be used and added as well. Virtual device drivers are devices that act like normal devices but are emulated by software. These virtual device do not physically exist, and thus do not control any real hardware. If a test site with only virtual devices is created, it can be used to perform completely virtual tests.
- Usable frequency range
- Maximum input power
Signal generator
Amplifier
Antenna
Coupler
Powermeter
Pre Wait time | The minimum time that should be waited before the measurements starts. |
Measure | The minimum amount of measurements that RadiMation® has to perform to determine if the <Max. Difference> condition is met. |
Wait time | The minimum time that RadiMation® should be waiting between each measurement. |
Max. Difference | The maximum difference that is allowed between the <Measure> measurement value(s); the highest and the lowest values are compared. |
Max. Measure | The maximum amount of measurements that could be performed by RadiMation®, before there is a final measurement value available (which could meet these conditions, or not). |
Field Sensor
Measurement setting panel
Axis setting panel
The Axis configuration is a generic driver setting panel. There are several (old) field sensors which don’t support the read out of an isotropic value: instead they provide the measurements values of all three axes separately. Using the ‘Software isotropic’ setting in the device driver can then activate that the measurement data of all three axes are being interpret and calculate to the isotropic value and have this isotropic value being return as the measured field strength. When the field sensor already supports the retrieval of the isotropic measurement value, often this value is also returned when the software option is being selected in the device configuration: both isotropic as software isotropic will return the isotropic value of the field sensor. This is depending on the device driver and used equipment.
AD converter
Injection device
Calibration Jigs
Current Sensor
Pre Amplifiers
LISN
Turn Table
Antenna Tower
Absorbing Clamps
Clamp positioner
Cables
Switch matrix
EUT Controller
RS-232 Setting
The RS-232 Communication settings are used to specify the RS-232 communication parameters, for the communication with a measurement device over RS-232. A lot of modern measurement devices are connected by USB, however very often then a Virtual RS-232 COMPort (VCP) is generated over the USB connection. In that situation also the RS-232 communication settings should configured.
COM Port | The COM port which RadiMation® has to use to be communicate with the measurement device. |
Baudrate | Allows to configure the baudrate that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
Data bits | Allows to configure the number of data bits that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
Parity | Allows to configure the parity bit that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
Stop bits | Allows to configure the number of stop bits that should be used to communicate with the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
Send termination | Allows to configure if and which terminator should be used during data transmissions to the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
Receive termination | Allows to configure if and which terminator should be used during the receiving of data from the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
Receiving a NewLine ends read | Allows to configure if a read should be ended as soon as the receive terminator is received from the measurement device. This setting can be a fixed device specific value, in which case it cannot be configured and then the setting will be disabled. |
GPIB Setting
Primary Address | The primary address specifies the address of the device, so if the device you want to configure is on address is on 20 you enter 20. Please consult the manual of the device how to determine the GPIB address of the device. |
Use advanced configuration | Allows the end-user to enables the more advanced configuration parameters. Those advanced option should only be used if the default settings are not sufficient enough. |
GPIB Board | With GPIB Board you can specify the GPIB board that is used. The default value is 0 and can only be different when multiple GPIB boards are present. |
Secondary Address | The second address is default 0, and should only be changed when needed. For further information please look in the help of National Instruments 488.2. |
GPIB Delay | GPIB delay is the delay between GPIB reading and writing actions. Some older IEEE 488.2 machines have difficulty communicating with fast PC's (> 2.5 GHz). This is most of the time noticeable when a driver is sometimes working and some times gives a GPIB (EABO or TIMO) error. These errors are most of the time, generated randomly. Specifying a GPIB delay time of 3000 uSeconds can fix these random errors. Run the test again and see of the problem as disappeared. Is the problem has disappear then your problem was timing, if not please contact your reseller and report the problems you are having. |
Clear device during initialisation | When checked, a low level GPIB command to reset the device will be send to the device during initialisation. |
Readdress device | When checked, a low level GPIB command to select the correct address will be transmitted every time a command is send to the device. |
VISA Settings
The VISA Communication settings are used to specify the VISA communication parameters, for the communication with a measurement device. The VISA library is a higher level communication library that supports different kind of communication methods. RadiMation® doesn't provide a VISA library itself, and thus requires that a VISA library from another supplier like National Instruments or Keysight Technologies is installed. The VISA manager that is provided by that VISA library can be used to determine the correct VISA resource. The selected VISA configuration thus also has influence if a measurement device is controlled by GPIB, RS-232, LAN, USB-TMC, VXI11, network-socket or another communication method .
Alias | Allows to specify a VISA Alias that should be used for the communication with the measurement device. Any Alias that is supported by VISA is accepted. The correct Alias can be determined by using the VISA manager (eg. National Instruments MAX) that is installed on the PC. |
GPIB | Allows to specify that GPIB should be used for the communication with the measurement device. The GPIB address of the measurement device should be specified. |
LAN | Allows to specify that a VXI11 or LXI connection should be used for the communication with the measurement device. It is possible to specify the IP-address or the (FQDN) hostname of the measurement device. |
RS-232 | Allows to specify that a RS232 (ASRL in VISA terms) connection should be used for the communication with the measurement device. The COM port of the measurement device should be specified. |
Visa-ID | Allows to specify a VISA Identifier that should be used for the communication with the measurement device. Any VISA Identifier that is supported by VISA is accepted. If one of the other communication methods is selected the corresponding VISA Identifier is also shown in this setting. Often used VISA identifiers are:
USB Settings
The USB Communication settings are used to specify that an USB connection to a DARE!! Instruments measurement device is used. It is not possible to use this USB communication setting for devices that simulate a Virtual COMPort (VCP) over an USB connection. The RS232 Settings should be used for such a kind of measurement device.
Device Identifier | The device identifier (which is an unique identifier of 8 groups of digits) that identifies the measurement device that is connected over USB. |
Detect | Will automatically determine the correct Device Identifier for the measurement device that is connected. |
TCPIP Settings
The TCPIP Communication settings are used to specify that a socket based TCPIP connection to a measurement device should be used.
Address | Allows to specify the IP-address or the (FQDN) hostname and the socket port number of the measurement device. This is normally done with a string like: "tcpip://<address-or-name>:<port-number>", where '<address-or-name>' is the IP address or hostname, and '<port-number>' is the socket port number on which the connection should be initiated. If the socket port number is a fixed port number, it is already shown as the default value, and it will be automatically added when no socket port number is specified. |
RadiMation® allows the user to create its own device drivers for test and measurement equipment, which is (not yet) implemented in the standard device driver list.
- Press the “New” button.
- Press the “Edit” button.
Generic settings
Start and stop frequency | The default value for the start frequency is 1 Hz and for the stop frequency is 120 GHz. The creator of the device is encouraged to set the correct start and stop frequency. If the start and stop frequency are set correctly, RadiMation® can warn the test engineer when he/she want to use the device out of its valid frequency range. |
Reset | In the reset window you need to specify the string that the software needs to send when it want to reset the device. For example *RST is commonly used reset string. If you don’t know the string then leave this window blank, and make sure that the device in a neutral state. |
Init | In the init window you need to specify the string that the software needs to send when it want to Init the device. For example *RST is commonly used reset string. |
Get ID | In the Get ID window you need to specify the string that the software needs to send when it want to get the ID string of the device. For example *IDN? is commonly used Get ID string. |
Returned ID | In the Returned ID window you need to specify the string that the software will receive so that it know that it has the right device. For example "Hewlett_Packard,8643A," can be used for the Hewlett Packard 8643A. If you leave this window empty then all returned strings are accepted. |
Set Frequency | Set Frequency is the string that needs to send to set the signal generator frequency. The unit is in MHZ, so the string should be made for MHz. |
Example: “FRQ__freq__MHZ”.
Example: “FRQ__freqHz__HZ”.
Example: “FRQ__freqkHz__KHZ”.
Example: “FRQ__freqMHz__MHZ”.
Example: “FRQ__freqGHz__GHZ”.
Set Carrier | Set Carrier is the string that needs to send to set the signal generator carrierlevel. The unit is in dBm, so the string should be made for dBM. |
Carrier on | Carrier on is the string that needs to send to set the signal generator carrier on. |
Example: “OUTPUT ON”.
Carrier off | Carrier off is the string that needs to send to set the signal generator carrier off. |
Example: “OUTPUT OFF”.
AM on | AM on is the string that needs to send to set the internal AM generator of the signal generator. The unit of frequency is KHz and the unit of Modulation Depth is %. |
AM off | AM off is the string that needs to send to set the internal am modulation of the signal generator off. |
External on | External on is the string that needs to send to set the modulator to the external input. |
External off | External off is the string that needs to send to set the modulator to the internal input. |
PM on | PM on is the string that needs to send to set the internal PM generator of the signal generator. The unit of frequency is KHz and the unit of duty cycle is %. |
PM off | PM off is the string that needs to send to set the internal PM modulation of the signal generator off. |
Sine Wave | Sine wave is the string that needs to be send when RadiMation® wants to set the wave form of the internal source to sine. |
Example: “SOURCE2:FUNC SIN”
Square Wave | Square wave is the string that needs to be send when RadiMation® wants to set the wave form of the internal source to square. |
Example: “SOURCE2:FUNC SQU”
The frequency range of the Chapter 15 as provided by the manufacturer is shown and selected as default. It is possible to overrule these frequencies and to manual adjust the allowed frequency range of the Chapter 15.
Be careful changing these setting as RadiMation® is no longer able to verify if the Chapter 15 is used outside frequency range that is specified by the manufacturer. This may result to serious damage of your measurement device.
Main
Use Remote Control and send specified commands | If the checkbox is ticked, the remote control of the amplifier will be used by using the specified commands. If the checkbox is not ticked, no commands will be transmitted to the amplifier at all |
Reset | The code that needs to be send to the device to initialize it in a defined state. When left blank, no command will be send. |
Init | The Init code that needs to be send to device. When left blank, no command will be send. |
Get ID | The code that needs to be send to device to get the identification back. A common used SCPI command is *IDN?. When left blank, no command will be send. |
Returned ID | The code that is send back as a return on the Get ID code. When left blank, no check will be performed. |
Deinit | The Deinit code that needs to be send to device. When left blank, no command will be send. |
Wait for Operation Completion after sending command(s) | If the checkbox is checked, every transmitted command will include a check to determine if the execution of the command is finished. |
Operation
Power On | The power on code that needs to be send to device. When left blank, no command will be send. |
Band Selection | The band select code that needs to be send to device. When left blank, no command will be send. |
Operate | The operate code that needs to be send to device. When left blank, no command will be send. |
Standby | The standby code that needs to be send to device. When left blank, no command will be send. |
Power Off | The power off code that needs to be send to device. When left blank, no command will be send. |
Delay after power on | The time that must be waited after sending the power on command. |
Delay after power off | The time that must be waited after sending the power off command. |
Example
Description | Command | Parameters |
Standby / Operate | OUT1 | 0 = RF STANDBY 1 = RF ON |
Band Selection | OUT3 | 0 = BAND 1 1 = BAND 2 |
Power off / on | OUT4 | 0 = LINE STANDBY 1 = LINE ON |
Set frequency | Set Frequency is the string that needs to send to set the powermeter frequency. The unit is in MHz, so the string should be made for MHz. |
Select Channel | Set Select Channel is the string that RadiMation® needs to send to set the powermeter channel. This is only necessary when the powermeter has more the one channel. |
Example: “P1,U1”.
Trigger | Trigger is the string that RadiMation® needs to send to trigger the powermeter. |
Example: “X1”
Result Format | Result Format is the string that RadiMation® needs to use to decode the value from the string send by the powermeter. The return value is interpreted in dBm. |
Example: “__result__”
Start Zero | Start Zero is the string that RadiMation® needs to send to start zeroing the powermeter. |
Example: “O1”
Duration | Duration is the time that RadiMation® waits so that the powermeter can zero properly. Make sure that this time is big enough, an incorrect value may result in unpredictable result. |
Initialisation and Check
Reset | The reset code that needs to be transmitted to device. When left blank, no command will be transmitted. |
Init | The command that is transmitted to initialise the configured device. When left blank, no command will be transmitted. |
Get ID | The query-command that is transmitted to retrieve the ID of the device. This is used to check if the device is connected. A commonly used SCPI command is: '*IDN?'. When left blank, no command will be transmitted. |
Returned ID | The expected response of the device on the Get ID query. The text that is specified will be searched in the real response on Get ID query. If the specified text can be found in the response, the check for the connection is successful, otherwise it is reported that the measurement device is not connected. Leaving this blank, will skip the check if the measurement device is connected, and it is always assumed that the device is connected. |
Deinit | Specifies the command that is transmitted when the device will not be controlled anymore.This can for example be used to put the measurement device in an intrinsic safe state. When left blank, no command will be transmitted. |
Wait for Completion after sending command | If the checkbox is ticked, RadiMation® will wait for all the commands to complete, before it continues. This is achieved by also transmitting the SCPI query-command '*OPC?' to the device, and waiting for the response. |
Channels
Trigger | The trigger query-command can be specified to trigger and request a new measurement value from the device. A commonly used SCPI query-command is: 'READ?'. |
Timeout ms | The timeout (specified in milliseconds) that should be used to read the response from the device. If no valid response is received within the timeout it is assumed that no value is read. |
Read Back | Different measurement devices will return the measured value in different formatting. The configurable AD convertor is able to determine the numeric value of the measurement device response by using regular expressions. The text in the Read Back box, is used as the regular expressions to determine the numeric value in the response of the measurement device.
Validate Expression | Shows a small window where the expected response of the measurement device and a regular expression can be typed. The specified regular expression will be used to interpret the specified result, and the result will be shown. This window can be used to test the regular expression, to determine if the expected response results in the desired value. |
Minimum value | The lowest value of the channel that can be measured with the controlled measurement device. The value must be the same as filled in the EUT window. It normally is the best to configure this value to be 0. |
Maximum value | The highest value of the channel that can be measured with the controlled measurement device. The value must be the same as filled in the EUT window. It normally is the best to configure this value to be 1. |
Read Back examples
Received information | Regular expression | Determined measurement value | Note |
U_L_N 325 | (-?[0-9.,Ee+-]+) | 325 | Takes the first number. |
I_L1;12.34 | ;(-?[0-9.,Ee+-]+) | 12.34 | Takes the first number after ";". |
THD_U_L1;;14,5 | ;;(-?[0-9.,Ee+-]+) | 14.5 | Takes the first number after ";;". |
AC_FREQ;Channel1;1.23E3 | ;.*;(-?[0-9.,Ee+-]+) | 1230 | Takes the first number after the appearance of a second ";". |
Input | Any text that is expected to be returned by the device. |
Regular Expression | The Regular expression that is being tested. This regular expression will be used to use the text from Input and convert it into a numerical value. |
Result | The numerical value that is determined by the device driver using the Regular Expression on the Input. |
Communication
Start Frequency | The lowest usable frequency of the device. |
Stop Frequency | The highest usable frequency of the device. |
Resistance | The impedance of the injection system itself, for which the calibration jig is used to calibrate it.
Configurable LISN
Reset | The reset command that needs to be send to device. When left blank, no command will be send. |
Init | The command that is send to initialize the configured device. When left blank no command will be send. |
Get ID | The command that is send to retrieve the identity of the device. This is used to check if the device is connected. A commonly used SCPI command is: *IDN?. When left blank, no command will be send, and the device check is skipped. |
Returned ID | A string that is used to check if the correct device driver is selected and the device is connected. The device check consists of a few steps. First the Get ID command is transmitted to the device, and the response from the device is then received. The received response is then searched for the string specified at Returned ID, and if the string is found it is confirmed that the correct device is connected. The string specified can also be a Regular expression, which is then used to find a match in the response from the device. Leaving this blank, will skip the device check, and it is silently assumed (but not checked) that the correct device is connected. |
Deinit | Specifies the command that is send when the device is no longer controlled. This can for example be used to put the measurement device is an intrinsic safe state. Leaving this blank, will keep the device in its last state after controlling it. |
Wait for Completion after sending command | The checkmark can be enabled so RadiMation® will wait for all the commands to complete, before it continues. This is done by sending SCPI command *OPC? to the device. |
Neutral | The command that should be transmitted when the 'Neutral' line of the LISN should be selected. If no command is specified, nothing will be transmitted. |
Line 1 | The command that should be transmitted when the 'Line 1' line of the LISN should be selected. If no command is specified, nothing will be transmitted. |
Line 2 | The command that should be transmitted when the 'Line 2' line of the LISN should be selected. If no command is specified, nothing will be transmitted. |
Line 3 | The command that should be transmitted when the 'Line 3' line of the LISN should be selected. If no command is specified, nothing will be transmitted. |
Ok | Closes the dialog, where all the changed settings are stored. |
Cancel | Closes the dialog, where all the changed settings are discarded. |
Communication | Opens an additional dialog which allows to set the correct communication medium to communicate with the device, including any relevant settings. |
Configurable commands
Reset | The reset code that needs to be send to device. When left blank, no command will be send. |
Get Id | The command that is send to retrieve the ID of the device. This is used to check if the device is connected. A commonly used SCPI command is: *IDN?. When left blank, no command will be send. |
Returned ID | The identifier is used to check if the correct device driver is selected and the device is connected. Leaving this blank, will skip the device check. |
Goto angle | The command that should be send to turn the turn table. The command must include the keyword __angle__, __degree__ or __radian__, which will be replaced by the desired destination angle for the turntable. |
Current Angle | This is the command to request the current angle of the device. |
Current angle format | This is a regular expression to obtain the current angle from the response of the Current angle command. See regular expression examples below. |
Movement ready | This is the command to request the current status of the turn table. This command is used to determine if the turntable is ready with the movement to the destination angle. |
Movement ready response | This should be the response from the device when the turntable is not moving/rotating anymore. |
Stop | This is the command to abort/stop any rotation. |
Order of executed commands
Check device
Device is initialised
Device is deinitialised
Retrieve the current angle from the turntable
Turn the turntable to an angle
Regular expression examples
Some examples are:
Received information | Regular expression | RadiMation® Readout | Note |
U_L_N 325 | (-?[0-9.,Ee-]+) | 325 | Takes the first number. |
I_L1;12.34 | ;(-?[0-9.,Ee-]+) | 12.34 | Takes the first number after ";". |
THD_U_L1;;14,5 | ;;(-?[0-9.,Ee-]+) | 14.5 | Takes the first number after ";;". |
AC_FREQ;Channel1;1.23E3 | ;.*;(-?[0-9.,Ee-]+) | 1230 | Takes the first number after the appearance of a second ";". |
Communication
Identification
Configurable Antenna Tower commands
Antenna Tower
Stop Movement | The command that is send to stop the antenna tower. When left blank, no command will be send. |
Current Height | The command that is send to request the current height. When left blank no command will be send. |
Current Height Format | A regular expression to parse the response from the Current Height request. The received value will be interpreted as being the the unit in Meter, Centimeter or Millimeter, as selected by the dropdownbox. |
Go to Height | The command that is send to move the antenna tower to a certain height. The command must include a keyword, __meter__, __centimeter__ or __millimeter__ which will be replaced with the corresponding height for the antenna tower. When left blank, no command will be sent. |
Position stopped | The command that is send to request the status if the antenna tower is moving. When left blank, no command will be send. |
Position stopped format | A regular expression which will be matched against the response of the Position stopped command. When the result is matching with the response, the tower is stopped. |
Current Polarization | The command to request the current polarisation. It is mandatory to also supply the format of the polarization in the next fields. When left blank, no command will be sent. |
Horizontal Polarization format | A regular expression which will be matched against the response of the Current Polarization command. When the result is matching the driver reports Horizontal back to RadiMation. |
Vertical Polarization format | A regular expression which will be matched against the response of the Current Polarization command. When the result is matching the driver reports Vertical back to RadiMation. |
Hor. Polarization | The command that is send to change the polarization to horizontal. When left blank, no command will be send. |
Vert. Polarization | The command that is send to change the polarization to vertical. When left blank, no command will be send. |
Pol Hor. stopped | The command that is send after the command Hor. Polarization is sent, with a delay of Waiting time between the two commands. When left blank, no command will be send. |
Pol Vert. stopped | The command that is send after the command Vert. Polarization is sent, with a delay of Waiting time between the two commands. When left blank, no command will be send. |
Waiting time | The wait time, specified in milli seconds, between the Polarization command and Polarization stopped commands. |
Antenna Tower Advanced
Ignore height change | When checked, no height related commands and changes will be send to the antenna tower. This can for example be checked if the the antenna is mounted on a fixed height tripod. |
Ignore polarisation change | When checked, no polarisation related commands and changes will be send to the Antenna Tower. This can for example be checked if the antenna tower does not have a automatic polariser. |
Move antenna before measurement | When checked, the antenna will be moved to the Start position before the actual test is started. |
Start position | The height, specified in centimeters, to which the antenna is moved, before the actual test is started. |
Move antenna after measurement | When checked, the antenna will be moved to the End position after the test has finished. |
End position | The height, specified in centimeters, to which the antenna is moved, after the test has finished. |
Wait time | The time, specified in seconds, to wait after a command is issued to change the polarisation. This can for example be used to include an additional delay to ensure that the antenna polariser has reached the final location before the actual test continues. |
Configurable Cable
Device Driver |
Operation |
Operation Complete |
Test |
Signal |
Dwell-time |
Modulation |
Measurements |
Antenna Tower |
Turntable |
keyword | inserted value |
__freq__ | the signal generator frequency expressed in MHz |
__freqHz__ | the signal generator frequency expressed in Hz |
__freqkHz__ | the signal generator frequency expressed in kHz |
__freqMHz__ | the signal generator frequency expressed in MHz |
__freqGHz__ | the signal generator frequency expressed in GHz |
__carrier__ | the signal generator carrier level expressed in dBm |
__carrierdBm__ | the signal generator carrier level expressed in dBm |
__carrierW__ | the signal generator carrier level expressed in Watt |
__carriermW__ | the signal generator carrier level expressed in milli-Watt |
__forward__ | the forward power expressed in dBm |
__forwarddBm__ | the forward power expressed in dBm |
__forwardW__ | the forward power expressed in Watt |
__forwardmW__ | the forward power expressed in milli-Watt |
__reflected__ | the reflected power expressed in dBm |
__reflecteddBm__ | the reflected power expressed in dBm |
__reflectedW__ | the reflected power expressed in Watt |
__reflectedmW__ | the reflected power expressed in milli-Watt |
__height__ | the height where the antenna is moving to expressed in metre |
__heightm__ | the height where the antenna is moving to expressed in metre |
__heightcm__ | the height where the antenna is moving to expressed in centimetre |
__angle__ | the angle where the turntable is turning to expressed in degrees |
__degree__ | the angle where the turntable is turning to expressed in degrees |
__radian__ | the angle where the turntable is turning to expressed in radians |
EUT Controller
Device Driver |
Operation |
Test |
Signal |
Dwell-time |
Modulation |
Measurements |
Antenna Tower |
Turntable |
__freq__ | The signal generator frequency expressed in MHz |
__freqHz__ | The signal generator frequency expressed in Hz |
__freqkHz__ | The signal generator frequency expressed in kHz |
__freqMHz__ | The signal generator frequency expressed in MHz |
__freqGHz__ | The signal generator frequency expressed in GHz |
__carrier__ | The signal generator carrier level expressed in dBm |
__carrierdBm__ | The signal generator carrier level expressed in dBm |
__carrierW__ | The signal generator carrier level expressed in Watt |
__carriermW__ | The signal generator carrier level expressed in milli-Watt |
__forward__ | The forward power expressed in dBm |
__forwarddBm__ | The forward power expressed in dBm |
__forwardW__ | The forward power expressed in Watt |
__forwardmW__ | The forward power expressed in milli-Watt |
__reflected__ | The reflected power expressed in dBm |
__reflecteddBm__ | The reflected power expressed in dBm |
__reflectedW__ | The reflected power expressed in Watt |
__reflectedmW__ | The reflected power expressed in milli-Watt |
__height__ | The height where the antenna is moving to expressed in metre |
__heightm__ | The height where the antenna is moving to expressed in metre |
__heightcm__ | The height where the antenna is moving to expressed in centimetre |
__angle__ | The angle where the turntable is turning to expressed in degrees |
__degree__ | The angle where the turntable is turning to expressed in degrees |
__radian__ | The angle where the turntable is turning to expressed in radians |
__polarisation__ | The antenna polarisation where the antenna is set to expressed as 'Horizontal' of 'Vertical'. |
__averagefield__ | The averagefield expressed in V/m. |
__calculatedfield__ | The calculated field expressed in V/m. |
__modulation__ | The current modulation as textual description of the applied modulation. For example: 'None', 'AM:1 kHz, 80%', 'FM: 1 kHz, 20 kHz' or 'PM: 200 Hz, 15%'. |
__modulationtype__ | The current modulation type, where this can be 'None', 'AM', 'FM' or 'Pulse'. |
__modulationfrequency__ | The modulation frequency expressed in Hz, if the modulation is active. |
__modulationfrequencyHz__ | The modulation frequency expressed in Hz, if the modulation is active. |
__modulationfrequencykHz__ | The modulation frequency expressed in kHz, if the modulation is active. |
__modulationfrequencyMHz__ | The modulation frequency expressed in MHz, if the modulation is active. |
__modulationdepth__ | The modulation depth that is being used by the AM modulation, if the AM modulation is active. |
__modulationdeviation__ | The modulation frequency expressed in Hz, if the modulation is active. |
__modulationdeviationHz__ | The modulation frequency expressed in Hz, if the modulation is active. |
__modulationdeviationkHz__ | The modulation frequency expressed in kHz, if the modulation is active. |
__modulationdeviationMHz__ | The modulation frequency expressed in MHz, if the modulation is active. |
__modulationdutycycle__ | The dutycycle expressed in %, if pulse modulation is active. |
__calculatedvoltage__ | The calculated current expressed in dBA. |
__calculatedcurrent__ | The calculated current expressed in A. |
__calculatedcurrentuA__ | The calculated current expressed in uA. |
__calculatedcurrentmA__ | The calculated current expressed in mA. |
__calculatedcurrentA__ | The calculated current expressed in A. |
__calculatedcurrentdBuA__ | The calculated current expressed in dBuA. |
__calculatedcurrentdBmA__ | The calculated current expressed in dBmA. |
__calculatedcurrentdBA__ | The calculated current expressed in dBA. |
__<InformationItemName>__ | The value of the corresponding EUT or General information item. |
Messages
Unknown Device Driver
GPIB: Device is not connected
Device not connected
How to Report an Error
When encountering a problem with the software you might would like to report it to the RadiMation support. The RadiMation error popups, contains detailed section. This can be expanded with details button on the error popup. In the expanded detailed error popup, a Report Error button is present. This allows Error Reporting to the RadiMation support within RadiMation. More information about Error Reporting can be found here: https://wiki.radimation.com/wiki/index.php/Error_Report
AD convertors
National Instruments 6023E 8 Analog inputs
Type of communication: IEEE.
Channels 1:
Hewlett Packard 34401A
Channel 1
Type of measurement: AC Volt
Minimum value: 0Volt
Maximum value: 1 kVolt.
Channel 2:
Minimum value: 0 Amp.
Maximum value: 3 Amp.
Channel 3
Type of measurement: DC Volt
Channel 4:
Maximum value: 3 Amp. (rms)
Channel 5
Minimum value: 0 Ω
Maximum value: 100 MΩ
Channel 6
Minimum value: 0 Hz.
Maximum value: 300 kHz
Channel 7 and 8
Not used
Hewlett Packard 54600
Channel 1:
Type of measurement: V Max.
Maximum value: 1000 Volt.
Channel 2:
Type of measurement: V Min
Minimum value: 0 Volt.
Channel 3
Channel 4:
Channel 5
Minimum value: 0 Hz
Maximum value: 100 kHz
Channel 6
Type of measurement: Period
Minimum value: 0 ms
Maximum value: 10000 ms
Channel 7
Minimum value: 0 ms
Channel 8
Minimum value: 0 ms
Hewlett Packard 3562A
Type of communication: GPIB
Channels
Minimum value: 0 dB
Maximum value: 100 dB
Hewlett Packard 59313
Channel 1
Minimum value: 0
Maximum value: 2048
Channel 2:
Minimum value: 0
Maximum value: 2048
Channel 3
Minimum value: 0
Maximum value: 2048
Channel 4:
Minimum value: 0
Maximum value: 2048
Channel 5 to 8
Not used.
Channels
Marconi 2305
Channel 1
Minimum value: 0
Maximum value: 1000 MHz
Channel 2:
Minimum value: 0
Maximum value: 1000
Channel 3 to 8
Not used.
Fluke 45 AC Current
Channels
Minimum value: 0 mA
Maximum value: 10.000 mA
Fluke 45 DC Current
Channels
Minimum value: 0 mA
Fluke 45 AC Voltage
Channels
Minimum value: 0 mV
Maximum value: 1.000.000 mV
Fluke 45 DC Voltage
Channels
Minimum value: 0 mV
Fluke 45 Frequency
Channels
Minimum value: 0 Hz
Maximum value: 1.000.000 Hz
Fluke 45 Resistance
Channels
Minimum value: 0 Ω
Maximum value: 100.000.000 Ω
LeCroy 9304AM Channel A,B,C,D
Channel 1
Maximum value: 353.55 Volt.
Channel 2:
Channel 3
Channel 4:
Maximum value: 707.1 Volt
Channel 5
Type of measurement: RMS
Maximum value: 250 Volt
Channel 6
Maximum value: 200 MHz
Channel 7 and 8
Not used
Fluke 8840A AC Current
Channels
Minimum value: 0 mA
Fluke 8840A DC Current
Channels
Minimum value: 0 mA
Fluke 8840A AC Voltage
Channels
Minimum value: 0 mV
Fluke 8840A DC Voltage
Channels
Minimum value: 0 mV
Hewlett Packard 3478A AC Current
Channels
Minimum value: 0 mA
Hewlett Packard 3478A DC Current
Channels
Minimum value: 0 mA
Hewlett Packard 3478A AC Voltage
Channels
Minimum value: 0 mV
Maximum value: 300.000 mV
Hewlett Packard 3478A DC Voltage
Channels
Minimum value: 0 mV
Tektronix TDS 400 Series
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Tektronix TDS 500A Series
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Tektronix TDS 600A Series
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
Tektronix TDS 3000 Series
Channels 1 to 4
Minimum value: 0
Maximum value: 100
Channels 5 to 8
Not used
DARE!! Development Radimate 2 and 3
Channels 1 to 8
Minimum value: 0
Maximum value: 16383
EIP 575
Channel 1
Minimum value: 0 Hz
Maximum value: 10 kHz
Channel 2:
Channel 3
Minimum value: 0 Hz
Maximum value: 1 MHz.
Channel 4:
Maximum value: 10 MHz.
Channel 5
Minimum value: 0 Hz
Maximum value: 100 MHz
Channel 6
Minimum value: 0 Hz
Maximum value: 1 GHz
Channel 7
Minimum value: 0 Hz
Maximum value: 10 GHz
Channel 8
Minimum value: 0 Hz
Maximum value: 100 GHz
Parallel Port Input 0x3BC and 0x378
Channel 1 to 8